Results 1 to 20 of 20
    Nov 2009
    Minsk, Belarus
    171
    15
    Two section vertical condenser
    Have two section vertical condencer with two inlet and two outlet conections.
    There are interesting question: how does arrange pipelines?
    I suppose that for properly condencer work, pressure drop of the sections with their connection pipes must be equal, but there is different heights in wich they situated.
    Could you check my solution please?
    In some places will have to think ...
    Oct 2005
    IRAN
    878
    Re: Two section vertical condenser
    Hi there,
    This kind of condensers are designed for two separate cycles (compressors), each section must be connected to one compressor.
    If you have one compressor and want to connect it to this condenser then there is no problem.
    If you have head pressure control (fan cycling) then you have to turn off/on the fans in pairs.
    Even Einstein Asked Questions
    Nov 2009
    Minsk, Belarus
    171
    15
    In my system there is one refrigeration cycle for two sections.
    Hot gas distribution must be the same in both sections. One section situated higher and condencing pressure will be less then in lower section.
    It's my opinion... could anybody tell about arrangement of pipelines in thise case? Or may be there is any recomendations?
    Oct 2003
    5,630
    34
    Aik, Lana, you can connect both together but I will have to make a schematic of it.
    This evening or tomorrow when I have a free day here in Belgium
    You have to use a siphon to overcome pressure difference.
    Or you may enter your discharge in the middle and split both with equal length to both coils and outlet both at the lowest part
    But with a siphon, you're sure.
    Or I can scan the relevant pages from Ind. Refr. from Stoecker.
    Nov 2009
    Minsk, Belarus
    171
    15
    Thanks a lot, Peter_1
    It would be good to see all about thise problem, because it's very interesting question for me. Really, now I don't understand some physics sides of thise question... and want to gain an understanding.
    May 2008
    66
    802
    Yo Peter, i would like to see yore solustion to. Can you sent me a copy?........please
    Ice
    Nov 2009
    Minsk, Belarus
    171
    15
    Sorry for persistence, could you scan the relevant pages from Ind. Refr. from Stoecker?
    Oct 2003
    5,630
    34
    Forgot this completely. Can you send me in PM your regular email please because I can't reduce it to a size allowed by this forum
    Sep 2003
    ISRAEL
    72
    4,248
    Hi Peter,
    you can try www.tinypic.com
    Oct 2003
    5,630
    34
    Nov 2009
    Minsk, Belarus
    171
    15
    Thanks Peter_1.
    Thise for ammonia systems or for refrigerant such as R404a, R22 and etc.?
    Oct 2003
    5,630
    34
    The natural phenomenas regarding pressure drop and pressure losses remains valid for every circulating liquid. So the solutions are valid for every refrigerant.
    Nov 2009
    Minsk, Belarus
    171
    15
    I have never seen equaliser line in nonammonia systems...
    Dec 2008
    Portugal
    48
    1,020
    Quote Originally Posted by Aik View Post
    If it's just one condenser with 1 circuit you will need it. Just make sure that discharge liquid line have a very very low velocity 0,3 m/s will more than sufficient so the vapor refrigerant can pass through the liquid without blockage this one.
    Dec 2008
    Portugal
    48
    1,020
    I'm sorry I meant "If it's just one condenser with 1 circuit you will not need it"
    Oct 2003
    5,630
    34
    Aik, have you ever tried to fill a bottle with streaming water where there's no possibility that air can escape out of the bottle to replace the filling water? This won't work.
    Or what if 1 l/s arrives in the receiver from eh codennser and only 0.8 l/s is leaving the receiver? (or in other words, more liquid coming in then going out of it) You will have a pressure buildup and the liquid will backup in the condenser.
    Dec 2008
    Portugal
    48
    1,020
    You can also communicate the upper part of the receiver (vapor) with the liquid separator/surge drum with pipe of very small cross section. The surge drum is connected to the LP, which is a much lower pressure and so the liquid receiver will be at a lower pressure than the condensers and so the liquid can be drained without a problem (no equalising line is needed). However with this method more energy is spent / less capacity plant because part of the vapour sucked by the compressor is from the HP, where it should be condensed.
    Nov 2009
    Minsk, Belarus
    171
    15
    Thanks a lot. I found thise handbook and understand all... very useful book.
  19. #19
    Oct 2003
    5,630
    34
    Quote Originally Posted by Sandro Baptista View Post
    As far as I understand this setup, there is no surge drum, this is a common DX setup with distance aircooled condensers. Your solution is not energy friendly and you describe anyhow an additional line to be installed
  20. #20
    Dec 2008
    Portugal
    48
    1,020
    This was just a response to AKI when he said:
    "I have never seen equaliser line in nonammonia systems..." so I just was tell him another possibilities.
  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Last Post: 15-01-2011, 01:24 AM
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. How to measure COP (evaporative condenser)