Thread: fujitsu fault codes
13-07-2010, 04:44 PM #1
fujitsu fault codes
Hi, I have a AOYR 12 LC system flasing twice on the timer led, any ideas
13-07-2010, 06:16 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: fujitsu fault codes
Outdoor unit does not have timer led.
Your error code means that indoor unit doesn't receive communication signal from outdoor unit.
13-07-2010, 06:53 PM #3
The timer led on the indoor unit is flashing twice. Chears
13-07-2010, 07:13 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
14-07-2010, 09:32 AM #5
andy1957
1. Check cabel conection indoor<->outdoor units
2. Check fuse 20A on outdoor unit
14-07-2010, 06:10 PM #6
found out that the fault is the out door board after talking with fujitsu tec dept. IE checked voltage on term 3 on the outdoor board the n tested it on the indoor board, both readings the same. \\\\going to remove the old system and fit a mitsi heavy inverter as i have had no trouble with them. Thanks to all
carrier fault codes
By richelli in forum Trouble ShootingReplies: 5Last Post: 18-06-2010, 07:35 AM -
fujitsu fault codes
By Andy AC in forum Air ConditioningReplies: 8Last Post: 06-03-2009, 03:38 PM -
Daikin fault codes
By Markie in forum Air ConditioningReplies: 16Last Post: 13-01-2009, 02:58 AM -
standardisation of fault codes?
By kelvin kline in forum Air ConditioningReplies: 1Last Post: 10-10-2007, 12:30 AM -
Fujitsu AOT24PMAL Fault Codes
By johnmart in forum Trouble ShootingReplies: 5Last Post: 19-04-2004, 06:39 AM
