Hello, I have a fujitsu AOU36RML1 Outdoor Heat pump connected to 4 ASU9RMLQ Indoor evap units and only one of the units will not blow cold air.
One of the four solenoids has been replaced already on the outdoor unit by our tech who installed the system.
We still can not figure out why just the one will not blow cold air while all others still do heat/ac fine after only being installed 8 months ago.
Any advice is appriciated, thanks.
-
13-07-2010, 02:19 PM #2
Re: Fujitsu Mini Split System A\C Problem
I also forgot that the valve was replaced along with the solenoid.
-
13-07-2010, 06:54 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Fujitsu Mini Split System A\C Problem
You also have strainer (which could be clogged) after expansion valve (that is not typical solenoid valve) and thermistor which is responsible for giving right data to logic circuit, which then operate electronic expansion valve.
Also, refrigerant charge must be checked and weighed in by instalation manual and according to actual total pipes length.
Than it could be conection cable to thermistor or expansion valve, or it could be control PCB fault.
-
13-07-2010, 03:41 PM #4
Fujitsu Split System A\C Problems
Hello, I have a fujitsu AOU36RML1 Outdoor Heat pump connected to 4 ASU9RMLQ Indoor evap units and only one of the units will not blow cold air.
One of the four solenoids and valve has been replaced already on the outdoor unit by our tech who installed the system.
We still can not figure out why just the one will not blow cold air, heat works good on it and the others still do heat/ac fine after only being installed 8 months ago.
Could the indoor unit be defective?
Any advice is appriciated, thanks.
-
14-07-2010, 03:33 PM #5
Re: Fujitsu Split System A\C Problems
Hello. Not working even with the 3 others switched off?
-
15-07-2010, 08:45 AM #6
Re: Fujitsu Split System A\C Problems
It sounds like an expansion expansion valve problem.
-
17-07-2010, 03:37 AM #7
Re: Fujitsu Split System A\C Problems
these units use an electronic expansion valve and they are clipped on right before the service valves on the condensing unit, they are crossed and u have to switch to correct line set this will remedy problem
-
17-07-2010, 03:41 AM #8
Re: Fujitsu Split System A\C Problems
p.s. I drink red wine
-
22-07-2010, 03:59 PM #9
Re: Fujitsu Split System A\C Problems
The one unit would not work even with all the others off. Fujitsu is replacing the whole outdoor unit since it is so new, and hopefully that remedys the problem.
We were able to get the one unit working that we needed by switching the "A" and "D" lines, luckily one room isnt occupied at the mement so that unit could be off. So it seems that the oudoor unit is just borked real bad haha, thank you for the replies and hopefully I dont have to post again with more problems
-
14-07-2010, 07:30 AM #10
Re: Fujitsu Mini Split System A\C Problem
The replaced valve (with solenoid) it is original parts?
-
22-07-2010, 04:08 PM #11
Re: Fujitsu Mini Split System A\C Problem
The replaced valve was an original part. After consulting with our tech and the fujitsu techs they dediced to warrenty the outdoor unit which hopefully fixes the problem. We were able to get the one unit working by switching the lines outside which thankfully kept the one office cold that we needed. The other office wasnt in use and that unit did not work once we switched the lines. Thanks for all the replies, hopefully the new outside unit fixes everything!
Similar Threads
-
Mini split load method
By Acrisoft in forum Air ConditioningReplies: 5Last Post: 18-12-2010, 02:33 PM -
Wiring to indoor mini split.
By Telstar_2112 in forum Air ConditioningReplies: 19Last Post: 06-07-2010, 10:00 PM -
problem in ammonia thermosyphon system
By ghanghas85 in forum Trouble ShootingReplies: 2Last Post: 08-06-2010, 03:56 PM -
Parallel oil system problem
By Tom C in forum Technical DiscussionsReplies: 3Last Post: 04-06-2010, 12:19 AM -
Migrate Oil problem - Medium Refrigeration System
By lurioda in forum FundamentalsReplies: 0Last Post: 24-02-2004, 06:20 AM