    Fujitsu Mini Split System A\C Problem



    Hello, I have a fujitsu AOU36RML1 Outdoor Heat pump connected to 4 ASU9RMLQ Indoor evap units and only one of the units will not blow cold air.
    One of the four solenoids has been replaced already on the outdoor unit by our tech who installed the system.
    We still can not figure out why just the one will not blow cold air while all others still do heat/ac fine after only being installed 8 months ago.
    Any advice is appriciated, thanks.



  2. #2
    Join Date
    Jul 2010
    Location
    VT, USA
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: Fujitsu Mini Split System A\C Problem

    I also forgot that the valve was replaced along with the solenoid.

  3. #3
    Join Date
    Jul 2010
    Location
    VT, USA
    Age
    36
    Posts
    5
    Rep Power
    0

    Fujitsu Split System A\C Problems

    Hello, I have a fujitsu AOU36RML1 Outdoor Heat pump connected to 4 ASU9RMLQ Indoor evap units and only one of the units will not blow cold air.
    One of the four solenoids and valve has been replaced already on the outdoor unit by our tech who installed the system.
    We still can not figure out why just the one will not blow cold air, heat works good on it and the others still do heat/ac fine after only being installed 8 months ago.
    Could the indoor unit be defective?
    Any advice is appriciated, thanks.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu Mini Split System A\C Problem

    You also have strainer (which could be clogged) after expansion valve (that is not typical solenoid valve) and thermistor which is responsible for giving right data to logic circuit, which then operate electronic expansion valve.
    Also, refrigerant charge must be checked and weighed in by instalation manual and according to actual total pipes length.
    Than it could be conection cable to thermistor or expansion valve, or it could be control PCB fault.

  5. #5
    Join Date
    May 2010
    Location
    Russia
    Posts
    168
    Rep Power
    15

    Re: Fujitsu Mini Split System A\C Problem

    The replaced valve (with solenoid) it is original parts?

  6. #6
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Fujitsu Split System A\C Problems

    Hello. Not working even with the 3 others switched off?

  7. #7
    Join Date
    Mar 2005
    Location
    New Zealand
    Age
    43
    Posts
    64
    Rep Power
    20

    Re: Fujitsu Split System A\C Problems

    It sounds like an expansion expansion valve problem.

  8. #8
    Join Date
    Dec 2009
    Location
    new york
    Age
    62
    Posts
    23
    Rep Power
    0

    Re: Fujitsu Split System A\C Problems

    these units use an electronic expansion valve and they are clipped on right before the service valves on the condensing unit, they are crossed and u have to switch to correct line set this will remedy problem

  9. #9
    Join Date
    Dec 2009
    Location
    new york
    Age
    62
    Posts
    23
    Rep Power
    0

    Re: Fujitsu Split System A\C Problems

    p.s. I drink red wine

  10. #10
    Join Date
    Jul 2010
    Location
    VT, USA
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: Fujitsu Split System A\C Problems

    The one unit would not work even with all the others off. Fujitsu is replacing the whole outdoor unit since it is so new, and hopefully that remedys the problem.
    We were able to get the one unit working that we needed by switching the "A" and "D" lines, luckily one room isnt occupied at the mement so that unit could be off. So it seems that the oudoor unit is just borked real bad haha, thank you for the replies and hopefully I dont have to post again with more problems

  11. #11
    Join Date
    Jul 2010
    Location
    VT, USA
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: Fujitsu Mini Split System A\C Problem

    The replaced valve was an original part. After consulting with our tech and the fujitsu techs they dediced to warrenty the outdoor unit which hopefully fixes the problem. We were able to get the one unit working by switching the lines outside which thankfully kept the one office cold that we needed. The other office wasnt in use and that unit did not work once we switched the lines. Thanks for all the replies, hopefully the new outside unit fixes everything!

Similar Threads

  1. Mini split load method
    By Acrisoft in forum Air Conditioning
    Replies: 5
    Last Post: 18-12-2010, 02:33 PM
  2. Wiring to indoor mini split.
    By Telstar_2112 in forum Air Conditioning
    Replies: 19
    Last Post: 06-07-2010, 10:00 PM
  3. problem in ammonia thermosyphon system
    By ghanghas85 in forum Trouble Shooting
    Replies: 2
    Last Post: 08-06-2010, 03:56 PM
  4. Parallel oil system problem
    By Tom C in forum Technical Discussions
    Replies: 3
    Last Post: 04-06-2010, 12:19 AM
  5. Migrate Oil problem - Medium Refrigeration System
    By lurioda in forum Fundamentals
    Replies: 0
    Last Post: 24-02-2004, 06:20 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •