    oversizing condenser fan motors?



    1/4 horse 1075 condenser fan motor replaced by a 1/2 condenser fan motor, does this pose a problem by spinning faster due to pitch of fan? i would like to think that this could cause over condensing problems. am i correct or am i wrong?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: oversizing condenser fan motors?

    Why does the fan spin faster! (excluding slippage) HP is not related to speed.

  3. #3
    Join Date
    Mar 2008
    Location
    England
    Posts
    232
    Rep Power
    20

    Re: oversizing condenser fan motors?

    Quote Originally Posted by delta T View Post
    1/4 horse 1075 condenser fan motor replaced by a 1/2 condenser fan motor, does this pose a problem by spinning faster due to pitch of fan? i would like to think that this could cause over condensing problems. am i correct or am i wrong?
    Speed in AC motors is related to the number of poles in the motor.

    2 pole motor at 50HZ has nominal speed of 2800 RPM

    4 pole motor at 50HZ has nominal speed of 1400 RPM

    6 pole motor at 50HZ has nominal speed of 900 RPM.

    These nominal speeds are a little less than the Synchronous speed due to slip.
    It is worth mentioning that most small condenser fan motors on packaged units are Shaded Pole

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: oversizing condenser fan motors?

    Quote Originally Posted by delta T View Post
    1/4 horse 1075 condenser fan motor replaced by a 1/2 condenser fan motor, does this pose a problem by spinning faster due to pitch of fan? i would like to think that this could cause over condensing problems. am i correct or am i wrong?
    No problem. The new motor will have less load than the nominal so less thermal load on it. Will probably have more "time of life"
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: oversizing condenser fan motors?

    high power consumption using a 1/2 hp motors,a costly replacement.why not replace the original.
    abet

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: oversizing condenser fan motors?

    Maybe they don't have in stock for fast delivery. The higher consumption should not be very high because the fan is the same so the shaft power absorbed should be nearly the same...and maybe this bigger motor maybe have a higher efficiency, even at part load.
    To make progress is never good enough, I want to do better and better and better

Similar Threads

  1. oversizing condenser fan motors?
    By delta T in forum Electrical
    Replies: 3
    Last Post: 14-07-2010, 04:58 AM
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. How to measure COP (evaporative condenser)
    By Juho in forum Technical Discussions
    Replies: 5
    Last Post: 04-06-2010, 07:08 PM
  4. Evaporative Condenser system COP
    By Juho in forum Commercial
    Replies: 0
    Last Post: 03-06-2010, 09:23 AM
  5. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •