    oversizing condenser fan motors?



    1/4 horse 1075 condenser fan motor replaced by a 1/2 condenser fan motor, does this pose a problem by spinning faster due to pitch of fan? i would like to think that this could cause over condensing problems. am i correct or am i wrong?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: oversizing condenser fan motors?

    The pitch of the fan blade will not make it spin faster. The RPM of the fan is set by the electrical supply frequency and the number of pole pairs in the motor.

    The fan blade pitch determines the amount of air the fan will move and the motor is usually sized to counter that duty against an external static resistance.

    If your new fan spins at the same rate as the one you have replaced and you are using the same impeller (fan blade), in the same installation, the only downside will be the extra energy consumed.

    P.S.

    No such thing as 'over condensing'. The effect is known as 'excessive sub cooling' - but I'm sure you know that
    Last edited by frank; 13-07-2010 at 07:54 PM.

  3. #3
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: oversizing condenser fan motors?

    Its like replacing a straight 4 with a V8, or a 2.5 litre with a 5.0 litre engine. As long as fits it'll still work and have enough spare capacity for extra passengers but sup more juice.

    The Higher powered motors are for larger fans on larger condensing units, like frank says it'll just consume a bit more juice than a smaller one. Its better to fit the next size up with the same rpm than the next size down.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: oversizing condenser fan motors?

    Quote Originally Posted by delta T View Post
    1/4 horse 1075 condenser fan motor replaced by a 1/2 condenser fan motor, does this pose a problem by spinning faster due to pitch of fan? i would like to think that this could cause over condensing problems. am i correct or am i wrong?
    Hi:
    and if you have head pressure control ,you should have no problem at all.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  2. How to measure COP (evaporative condenser)
    By Juho in forum Technical Discussions
    Replies: 5
    Last Post: 04-06-2010, 07:08 PM
  3. Evaporative Condenser system COP
    By Juho in forum Commercial
    Replies: 0
    Last Post: 03-06-2010, 09:23 AM
  4. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  5. small display cabinet keeps seizing up CF motors
    By paul_h in forum Commercial
    Replies: 8
    Last Post: 11-11-2007, 01:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •