Results 1 to 12 of 12
Thread: operation pressure
12-07-2010, 04:04 PM #1
operation pressure
Dear alls,
I would like to know how to determine the operation pressure (Low/High pressure) of a refrigeration cycle using R22 or R134a.
At my company, we control LP/HP of air-conditioner using R22 at: 4~4.2/18~20kgf/cm2. in near future, we will change R22 to R134s, so how to control the LP/HP of refrigeration cycle? Pls help me!
12-07-2010, 11:04 PM #2
Re: operation pressure
Hi, do not think in pressures but in temperatures.
13-07-2010, 07:11 AM #3
Just check the R134a Pressure- Temperature charts and findout the LP/HP of R134a Corresponding to the R22 operating pressures/ Temperatures.
13-07-2010, 07:37 AM #4
What do you control on the AC's with the pressures you mention?
13-07-2010, 01:01 PM #5
13-07-2010, 01:46 PM #6
You running at -6,5 to -5 degree C evaporation and 46,5 to 51 degree C condensation. Your pressure with R134a should read 2,3~2,4/12,1~13,5 bar.
This is your smallest problem probably, the largest is that you loose a lot of cooling power when change to a crappy refrigerant. I assume you keep your machinery.
13-07-2010, 03:16 PM #7
13-07-2010, 03:31 PM #8
Temperature will be same if your compressor is big enough.
14-07-2010, 06:09 PM #9
why the change from R22 to R134a ?
if it is because of the fase-out, you will be better to confert to R407C, you will loose about 3% performence.
Ice
16-07-2010, 01:59 PM #10
16-07-2010, 05:36 PM #11
16-07-2010, 08:02 PM #12
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
Pressure Increase Generated by the Compressor
By stephen.t in forum FundamentalsReplies: 12Last Post: 06-02-2008, 07:10 PM -
Screw compressor system losing oil differential pressure
By orm in forum Trouble ShootingReplies: 27Last Post: 27-10-2006, 03:19 AM -
screw compressor
By vinod in forum Trouble ShootingReplies: 9Last Post: 17-12-2005, 01:46 AM -
High pressure reading before and after condenser coil
By Cofreth in forum RefrigerantsReplies: 6Last Post: 18-11-2005, 04:30 PM