    Question dry fan coil unit



    who can help me to offer me the manufacturers of dry FCU(without condensate)? i need to know some information about this product. thx in advance.


    rgds
    lichuan



  2. #2
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: dry fan coil unit

    The easy answer is its down to the system design.
    The system needs to be selected to give the required duty with the cooling coil coldest point temperature above the dewpoint temperature of the air.
    ie if a chilled water fan coil was being selected with water entering at 8°C with an air on temperature of 21°Cdb and 15°C wb the coil shouldn't sweat as there is no latent cooling.
    Likewise if a dx selection is required then the condensing unit would be selected to give an evaporating temperature of around 8°C by down sizing the CU or using a larger FCU.

    BritCit

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: dry fan coil unit

    Hi Britcit,
    Thanks. You're right.
    Convention FCU is designed on the condition of 7C inlet and 12C return chilled water and take the dehumidification task. Simply changing the conventional FCU to dry condition is not a good way, there should be specific product for it. Dry FCU can have more flexible installation. I'm not sure if there is such product in Europe.

    rgds
    lichuan

  4. #4
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: dry fan coil unit

    Hi lichuan
    In the UK we only use high sensible units in computer or PABX rooms and these are usually designed with high air flow volume and a high water temperature.
    The important factor is still the water temperature. No matter what the coil design if it is at a low enough temperature it will sweat.
    The coil design needs to be considered in regards to the airflow volume as well as the room condition as the air condition and coil temperatures need to be considered through the coil to ensure that at no point throgh the coil do you get below the dewpoint temperature at the coil surface while maximizing the coil efficiency.
    Ergo close control or computer room units are not suitable for cooling your living room, they are way to big and noisey/

    Regards
    BritCit

  5. #5
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: dry fan coil unit

    Hi BritCit
    Big volume air and high water temp is not fit for livimg room.
    If using in living room,dry FCU must combine dedicated outside fresh air unit to supply dry cool air to the room to rid off latent heat. Dry FCU is only for the sensible so it need not too much air volume and work at low level noise.
    thx for your idea.

    rgds
    lichuan

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Smile Re: dry fan coil unit

    thanks for Dcasystem (this is not your name???)
    i'll contact them.

  7. #7
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: dry fan coil unit

    Hi David,

    I've sent my add by email to you. looking forward to your brochure. I'll study the products at first to confirm if there is potentials in China.thanks

    rgds
    lichuan

Similar Threads

  1. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  2. Lennox fan coil unit question
    By THERMOACC in forum Fundamentals
    Replies: 2
    Last Post: 17-02-2006, 10:31 PM
  3. heating coil in front of duct unit
    By cruzeiros in forum Air Conditioning
    Replies: 3
    Last Post: 13-02-2006, 11:32 PM
  4. Selecting Evaporator coil and condensing unit
    By Abe in forum Tools and Calculators
    Replies: 7
    Last Post: 04-04-2003, 03:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •