    qwestion about RH and heat rejection



    Hello
    The higher is the ambient air 's RH the better is heat rejection of the condenser isn't it?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: qwestion about RH and heat rejection

    I think that heat rejection of condenser is not affected with RH of air.
    http://www.youtube.com/watch?v=IbVmpWvBIB0
    Last edited by nike123; 11-07-2010 at 08:57 AM.

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by nike123 View Post
    Heat rejection of condenser is not affected with RH of air.
    Incorrect, (Wrong) the higher the RH , the hgher the density (Wrong). Great SHC and heat transfer properties (Wrong)
    As your fan is a fixed volume flow, then your air mass flow would increase.(Wrong)
    Of course I presume we are talking about air cooled condensers.
    How much of a practical difference, between 0% and 100% it could be a good few %.(Wrong)
    Think of it as a bit like alltitude. Right
    I AM WRONG
    Sorry Nike
    Last edited by mad fridgie; 11-07-2010 at 09:04 AM.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by mad fridgie View Post
    Incorrect, the higher the RH , the hgher the density. Great SHC and heat transfer properties
    As your fan is a fixed volume flow, then your air mass flow would increase.
    Of course I presume we are talking about air cooled condensers.
    How much of a practical difference, between 0% and 100% it could be a good few %.
    Think of it as a bit like alltitude.

    OK, that doesn't seem to coincide with what I concluded by adjusting RH on SIAHUCALC software. Could you check video I posted (in edited 1. post) and comment.

  5. #5
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by nike123 View Post
    OK, that doesn't seem to coincide with what I concluded by adjusting RH on SIAHUCALC software. Could you check video I posted (in edited 1. post) and comment.
    Hi Nike, did check (on coolpack), look at my edit.
    We live and learn.
    cheers
    Mad

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by mad fridgie View Post
    Hi Nike, did check (on coolpack), look at my edit.
    We live and learn.
    cheers
    Mad
    Mad in your own defence, you have presumed that you had a fixed volume of dry air then you added water vapour, then your density would increase, so would your pressure. Then your original presumbtions would be correct.
    The question should now be asked does increase in RH change your locallised air pressure?
    Mad Mad Mad (alter egos)

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by mad fridgie View Post
    Mad in your own defence, you have presumed that you had a fixed volume of dry air then you added water vapour, then your density would increase, so would your pressure. Then your original presumbtions would be correct.
    The question should now be asked does increase in RH change your locallised air pressure?
    Mad Mad Mad (alter egos)
    Now you talking with someone on same level.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by mad fridgie View Post
    I AM WRONG
    Sorry Nike
    .............

  9. #9
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: qwestion about RH and heat rejection

    Thank you
    So, making the air, entering the condenser, more humid, wont reduce the load on the latter : heat rejection would worsen, HP would increase.
    Last edited by Yuri B.; 11-07-2010 at 11:01 AM.

  10. #10
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by Yuri B. View Post
    Thank you
    So, making the air, entering the condenser, more humid, wont reduce the load on the latter : heat rejection would worsen, HP would increase.
    This is a slightly different question, if you add water to the air stream into the condenser, then the water will vapourize, making the the air cooler. This would certainly help in reducing condensing pressures.

  11. #11
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: qwestion about RH and heat rejection

    Yep, thats wy the make small water towers to cool down big volumes of refrig in condensors.
    Have two chillers in service contract, both are of the same cooling capacity (265 KW), one has a DX condensor other one is a thirth of the sise but has a watertower to help cooling the small DX condensor. So its thru, if you add water to the air for cooling the condensor, its helps a lot. See wat happens if you have a hot summer day, and the client cals you for help because his systems trips in overheating. Take a firm hose of water and spray it over the condensor wils it is operating. You will see that everything comes back to normal.

    Ice

  12. #12
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: qwestion about RH and heat rejection

    As this was such an interesting question (original), and I am free of Jack (JD), i have calculated a bit further, yes the density does drop, but the SHC does increases. The ratio is in favour of the SHC capacity, thus would very "slightly" beneifit the condenser with increased humidity.

  13. #13
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: qwestion about RH and heat rejection

    Hi there,

    Almost all places which have high Rh are placed near the seas or oceans. This means sea level altitude. At this altitude air density is higher than air in higher altitude. When air density is high, air mass flow rate will be higher for the same fan. This increases the condenser performance.
    BUT moisture in air does not have latent heat. If you spray liquid water on an air cooled condenser then heat transfer will be so much higher because liquid water has high latent heat.
    Moisture in air already lost its latent heat.
    When you calculate air cooled condenser and change RH from 10% to 90% you will see that there is negligible difference in performance.
    Cheers
    Even Einstein Asked Questions

  14. #14
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by lana View Post
    Hi there,
    Moisture in air already lost its latent heat.
    When you calculate air cooled condenser and change RH from 10% to 90% you will see that there is negligible difference in performance.
    Cheers
    I cant agry more on the 90% fact, but if you go from 10% to 100%, as i said, spray it whit a hose, than you will see a nice difference.

    Ice

  15. #15
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: qwestion about RH and heat rejection

    Spray it with hose means liquid water which has huge amount of latent heat and this will make a huge difference. We are talking about humidity of air which already lost its latent heat and became vapour.
    Even Einstein Asked Questions

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: qwestion about RH and heat rejection

    Quote Originally Posted by Yuri B. View Post
    Thank you
    So, making the air, entering the condenser, more humid, wont reduce the load on the latter : heat rejection would worsen, HP would increase.
    Nope! It will remain same.
    Dont confuse humid in the air with water. Humid in air is evaporated water. Therefore, latent heat in humid air is alredy absorbed (by water evaporation) and only sensible heat could be transferred to humid air.

  17. #17
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: qwestion about RH and heat rejection

    It's hard to believe you get 40c days Ice?

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  4. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  5. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •