Thread: 404a freezer

  1. #1
    premoctane's Avatar
    premoctane Guest

    Question 404a freezer



    need some help here. i have a 404 freezer walk in box that is giving me trouble. The unit is operating 18/260 psig on initial start up. when the fan kicks in pressures rise to 25/270 psig. while operating, the first row that is fed by the distributor nozzle start forming a snow blanket, causing my airflow to lower and loss of air flow eventually. The first row of the evaporator remains snowed back to the distributor nozzle, the remaining evap rows are dry. I replaced the expansion valve and installed a new frost termination/fan activation switch. Same results. The condensing unit is air cooled with a head master valve 180 psig. The valve is open to the condensing unit without signs of leaking. sight glass is clear.
    any suggestions as to what this may be?



  2. #2
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: 404a freezer

    It sounds to me that maybe your TX valve and distibutor may not be matched correctly.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 404a freezer

    Describe position of TXV and distributor (or make photo) and how much apart they are (in cm).
    Distributor must be positioned vertically. What is evaporator capacity and TXV make and model number? Orifice size?
    Take bulb of TXV in your hand and see if that make any difference after while on frost pattern of evaporator.
    Last edited by nike123; 11-07-2010 at 07:30 AM.

  4. #4
    premoctane's Avatar
    premoctane Guest

    Re: 404a freezer

    the txv is flared sporlan fse 1 1/2 ton - txv was replaced yesterday and dial inside distributor matched for 404A on installation. the unit worked fine for 2 years. its driving me crazy that only the distributor line and first row of the coil gets snowy and the rest of the coil is dry of snow and seems normal. I even blew out the evaporator. I thought there even may be something wrong with the single fan motor not blowing enough air but its rated for 1.4 amps and drawing 1.5 amps. I'm stumped.

  5. #5
    Chewman's Avatar
    Chewman Guest

    Re: 404a freezer

    Over charged???

  6. #6
    Join Date
    Jan 2007
    Location
    New Zealand
    Age
    42
    Posts
    50
    Rep Power
    18

    Re: 404a freezer

    head pressure is too high mate. R404a massively loses effciency after 250 psi.should be around 215-230..
    Your evap coil isnt fully flooded and you have very low suction pressure so id say you have the wrong size orifice or a blockage.

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: 404a freezer

    Air on the system due a possible recent service? The presence of air increase the discharge pressure.
    Blow the R404A circuit with nitrogen. May be as licencetochill said a blockage in almost circuits.
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    Jul 2010
    Location
    manchester
    Posts
    212
    Rep Power
    15

    Re: 404a freezer

    what make evap is it?
    some have a orifice in the distributor.
    ie an orifice for gas type i think buffallo trident is one of them.

    is may be a possibility or is there any kinks in the distributor.

  9. #9
    Join Date
    Mar 2008
    Location
    Manchester
    Age
    74
    Posts
    33
    Rep Power
    0

    Re: 404a freezer

    Assuming you have fitted a TEV and not a TV. Firstly check your superheat across the coil. This will confirm a starved coil so then check your valve it may be partially discharged or filter blocked.Also the external connection should really be after the bulb

  10. #10
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: 404a freezer

    is there a heat exchanger by any chance in the loop? they can implode,a dodgey CPR ? just a alternative to the TX.

  11. #11
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 404a freezer

    Sound as you got a restriction somewhere in the system.

    What you describe is typical for such situation

  12. #12
    Upnorth's Avatar
    Upnorth Guest

    Talking Re: 404a freezer

    Is the txv externally equalized. If so make sure the external line is clear. On a freezer a mop valve is the way to go also.
    Quote Originally Posted by premoctane View Post
    need some help here. i have a 40
    4 freezer walk in box that is giving me trouble. The unit is operating 18/260 psig on initial start up. when the fan kicks in pressures rise to 25/270 psig. while operating, the first row that is fed by the distributor nozzle start forming a snow blanket, causing my airflow to lower and loss of air flow eventually. The first row of the evaporator remains snowed back to the distributor nozzle, the remaining evap rows are dry. I replaced the expansion valve and installed a new frost termination/fan activation switch. Same results. The condensing unit is air cooled with a head master valve 180 psig. The valve is open to the condensing unit without signs of leaking. sight glass is clear.
    any suggestions as to what this may be?

  13. #13
    JoselitoUribe's Avatar
    JoselitoUribe Guest

    Re: 404a freezer

    Sometimes air on system can create a restriction on the TXV this can be happening to this system.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: 404a freezer

    Quote Originally Posted by licencetochill View Post
    head pressure is too high mate. R404a massively loses effciency after 250 psi.should be around 215-230..
    Your evap coil isnt fully flooded and you have very low suction pressure so id say you have the wrong size orifice or a blockage.
    I disagree completely.
    1. How you conclude that HP is too high? You don't know the ambient nor the air on of the condenser.
    2. How can a refrigerant - R404a in this case - lose its efficiency?
    3. Why at a sudden should it loose efficiency if the HP raises from 230 psi to 250 psi?

    I agree with the 2nd part of you post.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: 404a freezer

    Quote Originally Posted by Chewman View Post
    Over charged???
    Should this gives then all these phenomenas? I doubt.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: 404a freezer

    Quote Originally Posted by Lastguest View Post
    Assuming you have fitted a TEV and not a TV. Firstly check your superheat across the coil. This will confirm a starved coil so then check your valve it may be partially discharged or filter blocked.Also the external connection should really be after the bulb
    What difference should it make if a TV instead of TEV?
    The SH over the coil can be OK but the coil can partially be starved.
    Why must the ext. connection be installed after the bulb? Isn't it even better that it is installed just the opposite way? Giving the fact that you speak about TEV an TV, I assume you're referring to Danfoss valves?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: 404a freezer

    To summarize:
    Air in the system will not starve you coil partially, it will increase HP and discharge temperature.
    No or wrong orifice in distributor.
    Distributor not facing up or down.
    Blocked capillary tube from distributor to coil.
    The TEV can't be the problem, all rows should then be starved or flooded.

    You have to measure every circuit in your evaporator on the same place to see which circuit is blocked.

    Other possible cause: once circuit has no load (ice on that circuit, perhaps on the inside of the evaporator) or the fan isn't blowing on that circuit. This not loaded circuit is flooded and the TEV bulb senses this and closes therefore all the other circuits, trying to maintain the SH of this one , almost not loaded circuit. Resulting in one circuit which seems working but on a very low evaporating temperature because the evaporator is working on only one of its partially loaded circuits.
    This phenomena happens when one row is freezing horizontally, mostly the upper or the lower part of the coil
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: 404a freezer

    i agree we need to know the ambient temp ,but there seems to be a inbalance between the suct/dis pressures,wheres the man with the answers anyway.!

  19. #19
    Join Date
    May 2005
    Location
    newbury
    Age
    43
    Posts
    13
    Rep Power
    0

    Re: 404a freezer

    sounds to me like you may have oil choking part of the coil or distributor.
    check the iol level in the compressor.

  20. #20
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: 404a freezer

    hi u said that u have changed the exp what about filter drier

Similar Threads

  1. Maytag Freezer TOO Cold (and fridge also)
    By ptb626 in forum Domestic
    Replies: 1
    Last Post: 17-08-2010, 01:56 PM
  2. Charging 404A into a new walk-in freezer
    By handyhusband01 in forum Commercial
    Replies: 17
    Last Post: 09-06-2010, 11:04 PM
  3. Blast Freezer Within Freezer
    By rickmor in forum Technical Discussions
    Replies: 4
    Last Post: 18-06-2009, 03:37 AM
  4. delta t for 404a in -21 upright freezer?
    By b-cool in forum Refrigerants
    Replies: 5
    Last Post: 12-03-2009, 12:35 PM
  5. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •