    Hi anybody got a quick rule of thumb I can use for sizing up a room/conservatory for air-con.
    Only need a rough guide based on floor area.
    Thanks Morph
  2. #2
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Re: Sizing aircon
    I was about to add my tuppance worth, until you said, conservatory!!
    Wot.................Conservatory!!!!!! ????
    This topic has been covered to death before, if only I can find the darned link!!
    take length and width in feet, multiply by 150 , that gives you Kw rating.
    Dont ask me how it works, it does somehow. But that rule applies to normal rooms, not conservatories and all those unusual glass cladded south facing places stuffed with a thousand people high on ecstacy and swinging their bodies about.
    hope that helps!!
    Terra
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Re: Sizing aircon
    I forgot to say as well............ask B& Q how to do it, ie: size up one of their systems for conservatory
    If that dont work, the wholesalers will be only too happy to help.
    Good luck
  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20
    Smile Re: Sizing aircon
    50w/cubic metre
    and some common sense.
  5. #5
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23
    Re: Sizing aircon
    For a standard room i would use 150w/m2 or 50btu/ft2
    for a computer room or PABX room 190w/m2 or 60btu/ft2
    However a conservatory isn't so easy as it depends on the buid and orientation. for North and west the 190w/m2 is probably ok but for south/east it is better to give the wholesalers the full details - glass area/ orientation, material ect and get them to size it for you
    BritCit
  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Re: Sizing aircon
    email me at dcoles@powercold.com and I'll send you a simple formula you can use in most cases.
    Why not post the formula so that we can all benefit
  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Re: Sizing aircon
    I'm sorry, but that is double dutch (sorry peter) to me. I.ve written it down but it does not make any sense.
    Is that an English expression Frank? Never heard of it before.
    What does it mean anyway
  8. #8
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    20
    Talking Re: Sizing aircon
    If you ask thumb rule 10fx10fx10f=1000sq/ft=1ton or around 12000 BTU at 42c ambient at 30% RH , increase
    in RH will lead to better efficency of the A/C. Try it out
    it will work perfectly in tropical climate.
  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Re: Sizing aircon
    How are you able to edit my post Peter?
    Double dutch is an expression we use to mean " it does not make much sense" - i.e. like trying to understand your mother tonge posts when we don't speak your language
  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Re: Sizing aircon
    Ohhhh.... sorry for that Frank, that was not my intention at all.
    These are the privileges of the moderators.
    I must have pushed on the edit button instead of the reply,..again...sorry,... this was not my intention.
    Can your remember the original post Frank so that it can be corrected again?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
  11. #11
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27
    Re: Sizing aircon
    Oh dont worry Peter.............it happens.......
    wasnt the first and definately wont be the last.....
    Frank, dont read too much into the Double Dutch thingy.............chill!!!
  12. #12
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19
    Re: Sizing aircon
    AC calc by cliksoftware still gets my vote, mine is version 2.8 and still works fine, I was going to update it to the latest copy but I cant see the point, the only thing it does not work out correctly is conservatories but that is what rule of thumb is all about and I have not sized one yet that does not work.
  13. #13
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19
    Re: Sizing aircon
    Quote Originally Posted by Morph
    Thanks Morph
    Length x width x height x 90 watts per cubic metres = required duty or length x width x 300 watts per square metre = required duty, I always work them out both ways and go for the bigger duty, always better to be safe than sorry.
  14. #14
    Join Date
    Sep 2005
    Location
    Australia
    Age
    68
    Posts
    7
    Rep Power
    0
    Re: Sizing aircon
    If you are going to do correct calculations you will need ambient conditions for the area before you can do anything else. I will not even try to enter the discussion using tons and BTU's..forgot those years ago.
  15. #15
    Qualitairsl's Avatar
    Qualitairsl Guest
    Re: Sizing aircon
    Panasonic offer a simple(ish) calculator on their .com website
  16. #16
    Join Date
    Oct 2005
    Location
    In a 2 bedroom unit. Why's That? :)
    Posts
    314
    Rep Power
    19
    Re: Sizing aircon
    question. Why do people still use IP instead of SI units.
    I thought the metric system was introduced to the US 5 yrs ago?? There is a chart I've been trying to get hold of that the old SEQEB had for room sizing.
    I've been told .075kw/m2 + .025kw/m2 for each half door window. If higher than 8" ceilings add .025kw/m2 for each meter above.
    Seems to be close on small applications. Does not take into consideration insulation etc etc etc.
    I think DOE2 programs does the calc?
    If anyone knows where I can get the table please email me at refrigerationmagnet@lycos.com
  17. #17
    Join Date
    Oct 2005
    Location
    Posts
    314
    Rep Power
    19
    Re: Sizing aircon
    The Australian energy rating department recomends 125watts/m2 in living areas and 80watts/m2 in bedrooms.
    Question. is there any posible way of working out KW cooling/heating cap when only given a Horsepower rating? I know the conversion but that is only motor kw not capacity no?
  18. #18
    Join Date
    Sep 2006
    Location
    Bribie Island , Queensland
    Age
    61
    Posts
    19
    Rep Power
    0
    Re: Sizing aircon
    Not sure about Australian Energy standards but those specs won't cut it in Queensland,
    155- 200 watts per square metre depending on heatload.
    Sure those standards will save power but they won't cool the rooms unless it's night time.
  19. #19
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18
    Re: Sizing aircon
    Quote Originally Posted by Morph View Post
    Thanks Morph
    Hi Morph,
    Please take note that RULE OF THUMB FIGURES should never be used for huge places with so many factors that may affect the cooling load e.g. glass walls, glass windows, skylight, building walls, ventilation/infiltration load, etc.
    Please check this one:
    http://www.refrigeration-engineer.co...7&postcount=11
    I hope i have shared something that could be valuable. . .
    Regards,
    Winfredy
  20. #20
    Join Date
    Dec 2006
    Location
    England
    Age
    69
    Posts
    35
    Rep Power
    0
    Re: Sizing aircon
    Whenever someone asks me for a unit for a conservatory I first ask why they think they one one, most say to stop it getting too hot whilst they are out! Then I tell them how much it would cost to run the largest wall mount we can get (8kw) and ask if they are still interested, most say they only want to spend less than £500.00 so it's off to B&Q to buy a waste of energy portable.
  21. #21
    Join Date
    Jun 2007
    Location
    Derby
    Age
    56
    Posts
    7
    Rep Power
    0
    Re: Sizing aircon
    Well I don't know about anyone else, but I've done several of the suggested calcs on a standard model & have come up with wildly varying results!
    The standard model I'm using is my appartment in the Algarve, which is roughly 8m x 6m with an average ceiling height of 3m open plan. Max ambient mid 30's.
    I'm gonna bung a 7-8 kw inverter in it. Anyone see any problem with that?
  22. #22
    Join Date
    Feb 2007
    Location
    Spain
    Age
    45
    Posts
    26
    Rep Power
    0
    Re: Sizing aircon
    Try using this great little app for converting, Area, Units, Power, Ect I use it alot its a very usefull program and its free.
    Link:
    http://www.52-chevy.net/pawprint/versaverter.zip
    I dont use this for making the calculation for what size unit I should be using its not for that but I tend to use:
    1) rooms that dont generate to much heat 120w * m2
    2) rooms that can get quite warm 150w * m2
    3) rooms that get very warm 190w * m2
    Then use, Versaverter to convert into BTUs, KW's, Kcal, HP, Ect.
    Also you need a little comonsense as well, after doing this for a while you can normally tell as soon as walk into a room and asking a few questions. Large rooms though def do more work on and make sure its correct. beter to go slightly over size than under, be safe not sorry.
  23. #23
    Sid Jones's Avatar
    Sid Jones Guest
    Re: Sizing aircon
    Thanks Morph
    Try 120 watts per square meter.
  24. #24
    Sid Jones's Avatar
    Sid Jones Guest
    For your normal apartment requirements 120 watts per square metre should do the trick. I am practicing in South Africa and it works for me.
    Good luck regards.
    Sid Jones.
  25. #25
    Join Date
    May 2007
    Location
    NC
    Posts
    262
    Rep Power
    18
    Re: Sizing aircon
    Shouldn't we be discouraging rules of thumb? Shouldn't we be pushing doing it the correct way. Seems like a bad idea to get something like that wrong in such a big application. Just my opinion.
  26. #26
    Join Date
    Jun 2007
    Location
    Derby
    Age
    56
    Posts
    7
    Rep Power
    0
    Re: Sizing aircon
    Cheers Sid, 6Kw sounds reasonable to me!
  27. #27
    Join Date
    May 2003
    Location
    Edmonton alberta Canada
    Posts
    95
    Rep Power
    22
    Re: Sizing aircon
    Thanks Morph
    Here we use 400 sq ft per ton
    wesmax
    Wes Maxfield
  28. #28
    Join Date
    Sep 2007
    Location
    Philippines
    Posts
    12
    Rep Power
    0
    Re: Sizing aircon
    in the philippines common conversion of capacity per area is : 550 ~ 650 Btu / m2 depending on the application.
  29. #29
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18
    Hi all
    Said this before but, I dont generally dont do rule of thumb when sizing, but when i do i never go below 125w per square meter in an office / domestic install and between 250w and 400w per square meter for conservatories depending on which way they face.
    If in doubt always ask some one who knows, most suppliers will size for you on the back of maybe getting an order.
    I tend to normally advise a 5kw inverter heat pump as they are normally on manufacturers smaller chasis, neater looking and lower price bracket, which would provide ample heating in winter and cooling for 95% of the UK summer, even on the hottest day it would cool the conservatory to an aceptable temperature to sit in.
    Thats my thoughts any way
  30. #30
    Join Date
    Aug 2005
    Location
    uk
    Posts
    45
    Rep Power
    0
    Re: Sizing aircon
    Hi,
    For me 12000 Btu is enough coz we have always low ambient temperature.Correct me if im wrong.
    Cesar
Similar Threads
  1. Piping and line sizing in lbs/min
    By Kathleen in forum Tools and Calculators
    Last Post: 29-05-2009, 03:07 PM
  2. crazy 3rd-world idea: aircon from small fridge
    By lsemprini in forum Fundamentals
    Last Post: 29-05-2008, 01:10 AM
  3. Compressor sizing using R404a
    By PCL in forum Refrigerants
    Last Post: 14-08-2006, 11:09 PM
  4. dunham-bush split aircon unit
    By philly in forum Air Conditioning
    Last Post: 06-07-2006, 10:24 PM
  5. Sizing for Australia
    By dogma in forum Fundamentals
    Last Post: 17-03-2006, 10:05 AM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts