    issues running a 2 ton compressor on a 1 1/2 ton cond. coil



    Hello all, new here.
    Just had a quick question, at work i have run into a couple condensing units (r22, residential) that have been previously "rebuilt" by, well, who knows. They have installed 2 ton compressors onto the existing 1.5 ton condensing coils.(pretty small ones at that)
    Basically, there is no way to get these units to run even close to normal, correct?
    Ok suction press and way high head press on the one unit, with close to "normal" readings on the other.
    Both with only about 6-8* delta t at the A coils.
    Unfortunately these are both on 3rd floor apts....
    My Maintenance Supervisor has less knowledge than me on AC systems and has a hard time understanding that this setup will not work properly. Oh, one has a 2 ton A-coil and the other a 1.5, if it matters.
    Am i correct here?
    Thanks in advance.

    Adam



  2. #2
    Join Date
    Jan 2010
    Location
    house
    Posts
    6
    Rep Power
    0

    Re: issues running a 2 ton compressor on a 1 1/2 ton cond. coil

    im also interested in this topic since my client asked me to replace a copeland scroll 2tonner compressor installed in a 1.5tonner tecumseh condenser, now since the compressor is already broken, i am inclined to replace it with a 2 ton hermetic piston compressor or use a 1/5ton piston compressor?

    thanks also in advance for any comments or advise.

  3. #3
    Join Date
    Apr 2008
    Location
    phillippines
    Posts
    125
    Rep Power
    17

    Re: issues running a 2 ton compressor on a 1 1/2 ton cond. coil

    definitely will not work,although the unit may run but will have a high head pressure
    and, low suction pressure on the other hand equating to low cooling capacity and high power consumption.compresor will not last long.
    abet

  4. #4
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: issues running a 2 ton compressor on a 1 1/2 ton cond. coil

    Quote Originally Posted by mo'parts View Post
    Hello all, new here.
    Just had a quick question, at work i have run into a couple condensing units (r22, residential) that have been previously "rebuilt" by, well, who knows. They have installed 2 ton compressors onto the existing 1.5 ton condensing coils.(pretty small ones at that)
    Basically, there is no way to get these units to run even close to normal, correct?
    Ok suction press and way high head press on the one unit, with close to "normal" readings on the other.
    Both with only about 6-8* delta t at the A coils.
    Unfortunately these are both on 3rd floor apts....
    My Maintenance Supervisor has less knowledge than me on AC systems and has a hard time understanding that this setup will not work properly. Oh, one has a 2 ton A-coil and the other a 1.5, if it matters.
    Am i correct here?
    Thanks in advance.

    Adam
    Hi Mo,parts,


    These sysrems have a capillary and you will need to replace the capillary. Change the capillary as per the kcal/hr of the unit and subcooling (the limiting factor will be the condenser)
    I have recently done a compressor replacement and did a cap change based on this rotary compressor manual.
    You then charge this system to the subcooling and finish the charge at the target superheat.
    You will find the formula for target superheat posted by Nike123 on this site.
    Due to size limitations on this site i cannot post it here.
    If you PM me your email id i will send you the attachment.

    Forum mates is there a way to post the manual omn the forum?

    Regards.
    Kssoin

Similar Threads

  1. coil sizing - custom project..
    By cadillackid in forum Heat Pumps
    Replies: 0
    Last Post: 24-04-2010, 07:57 PM
  2. AHU Calculations
    By SUBCONTRACTOR in forum Fundamentals
    Replies: 20
    Last Post: 07-11-2009, 04:51 AM
  3. About 2 stage coil
    By cstyx in forum Technical Discussions
    Replies: 3
    Last Post: 09-04-2009, 08:26 PM
  4. removing humidity
    By Sledge in forum Air Conditioning
    Replies: 31
    Last Post: 22-06-2007, 05:40 AM
  5. DX coil distributor issue
    By Lc_shi in forum Fundamentals
    Replies: 2
    Last Post: 16-11-2005, 01:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •