    Hi everybody. I have a Danfoss VLT 6000 variable speed drive that is tripping on ground fault all the time. I have checked the motor,cable and earth connection which all seems o/k. Is there anything else that can cause this alarm(Trip)
    Regards Ettienne



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Ettienne

    have you tried runing the inverter with the motor disconected if it works then check motor with a meger

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Ettienne

    Quote Originally Posted by Ettienne View Post
    Hi everybody. I have a Danfoss VLT 6000 variable speed drive that is tripping on ground fault all the time. I have checked the motor,cable and earth connection which all seems o/k. Is there anything else that can cause this alarm(Trip)
    Regards Ettienne
    Hi :
    possibly a very long motor cable could cause this symptom!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Ettienne

    Low motor insulation. Check it with a megger.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Ettienne

    Disconnect the VFD and run the motor straight on the mains and verify if problem persists. You then can make conclusion if there's a fault in the VFD.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Ettienne's Avatar
    Ettienne Guest

    Re: Ettienne

    Hi everyone, the motor runs perfecly without the VFD connected. When the drive tripps and is reset it will run for a couple of hours before it tripps again. Kind Regards Ettienne

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Ettienne

    Quote Originally Posted by Ettienne View Post
    Hi everyone, the motor runs perfecly without the VFD connected. When the drive tripps and is reset it will run for a couple of hours before it tripps again. Kind Regards Ettienne
    Hi:
    as i said before check your cable lentgh!this could cause high ground capacitance and drive tripping,try to run it with ground fault disabled ,while you are monitoring it if this stops the nuisence tripping ,change to a shielded cable! this will help.
    let us know how it goes!
    good luck