    Excessive superheat overheating compressor



    Hello

    Small bespoke domestic fridge system, approx 15m run to condensing unit along warm external wall. R407C -7 / 3.5 bar LP (Approx) set point 3c

    Compressor cycling on thermal protection.

    I've opened the expansion valve to 7k superheat measuring the suction pipe temperature AT THE COMPRESSOR, this has kept the compressor cold and all running well.

    I am unable to take a pressure at the evaporator and I'm worried by opening the TEV (internally equalised) the compressor will flood in very cold weather.

    All thoughts welcome

    Thanks
    Last edited by Contactor; 07-07-2010 at 12:03 AM. Reason: Added 'internally equalised'



  2. #2
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Excessive superheat overheating compressor

    Prior to opening the valve superheat at the compressor inlet was approx. 23k with pipe temp of about 16c
    Last edited by Contactor; 07-07-2010 at 12:09 AM.

  3. #3
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Excessive superheat overheating compressor

    Hello contactor

    You say
    opened the expansion valve to 7k superheat
    what was it before and what temp was your fridge?

    AND what is the superheat when it gets down to setpoint?
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  4. #4
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Excessive superheat overheating compressor

    So if for example, the outdoor temperature fell to -10, the compressor could presumably be flooded by a 2 phase mixture reduced to liquid sub cooled by 3k ?
    Last edited by Contactor; 07-07-2010 at 12:18 AM.

  5. #5
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Excessive superheat overheating compressor

    thanks for your reply trash, i think my edits crossed with your post -

    fridge was up to 17c temp while cycling on thermal protection

    you make a good point about measuring the sh at set point, i'm not sure about that one

  6. #6
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Excessive superheat overheating compressor

    So if for example, the outdoor temperature fell to -10, the compressor would presumably be flooded by a 2 phase mixture sub cooled by at least 3k 07-07-2010 12:08 AM
    So if for example, the outdoor temperature fell to -10, the compressor would presumably be flooded by a 2 phase mixture sub cooled by at least 3k
    Not neccessarily and maybe not at all. That wouuld depend on what load you got and how your TXV copes and of course you will have the condensor to consider.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  7. #7
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Excessive superheat overheating compressor

    wouldnt measuring superheat temp at evap with thermometers be more accurate and is the suction line well insulated?i dont know about using 407c for this application either?
    mmm to beer or not to beer...........lets drink breakfast

  8. #8
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Excessive superheat overheating compressor

    system was commissioned to 7k superheat at evaporator but this wasn't enough to keep the compressor running. The suction line is insulated in 3/8'' black armaflex, but I wondered if this is only making matters worse in the blazing sun as it seems to get very hot.

  9. #9
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Excessive superheat overheating compressor

    wouldnt measuring superheat temp at evap with thermometers be more accurate and is the suction line well insulated?
    Valid points

    dont know about using 407c for this application either?
    I must admit I'm more AC than fridge but evaporating at -7c doesn't sound bad for 407c or is there something I'm not getting?
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  10. #10
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Excessive superheat overheating compressor

    system was commissioned to 7k superheat at evaporator but this wasn't enough to keep the compressor running.
    Under what load?

    16K superheat just from the suction line
    Last edited by TRASH101; 07-07-2010 at 12:59 AM. Reason: too mucking fuddled
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  11. #11
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Excessive superheat overheating compressor

    i was of the belief that 407c was high temp refrigerant,dunno havent played with the stuff yet.are the current draws in range if not maybe check for non condesables,condenser air flows,run capacitor etc.
    3/8 wall does sound to thin i now use 19mm wall on medium temp stuff and have done so since the tirade of new refrigerants.
    mmm to beer or not to beer...........lets drink breakfast

  12. #12
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Excessive superheat overheating compressor

    you say it was commissioned to 7 kelvin was this on 407c or 22 if the later then your condenser size is probably to small,was always under the impression that 407 ran a higher head.
    might pay to fit schraeder and reprocess system.
    mmm to beer or not to beer...........lets drink breakfast

  13. #13
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Excessive superheat overheating compressor

    You have got to find out what is going on with the suction line. Even uninsulated it shouldn't gain 16k over 14m of pipe.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  14. #14
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Excessive superheat overheating compressor

    SORRY IT'S 404A !!!!!! my typo, sorry!!

    maybe my temps are out slightly, also I only measured them twice and at the same time in the cycle, but generally the SH was high.

    This fridge is made of bricks, it's an old archway in a cellar in a big old house with a made to measure steel framed double glazed fridge door on it, it was empty so very low load

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Replies: 3
    Last Post: 29-10-2009, 09:41 PM
  3. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  4. how do you determine what the superheat should be on a system
    By frosty74 in forum Supermarket Refrigeration
    Replies: 13
    Last Post: 21-05-2009, 05:13 PM
  5. How do you calculate Superheat?
    By zolar1 in forum Training
    Replies: 39
    Last Post: 10-05-2002, 02:37 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •