    could anybody explain how we find out if theres sufficient air flow by checking delta T ? EG how does 2 temp readings tell you if theres correct airflow across an evap or condenser?
    thanks .



  2. #2
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: delta T

    Does anybody know of any books with the above info in then?
    Can you get Garys book over here in England?

  3. #3
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: delta T

    When air at certain temp flows through a heat exchanger such as evaporator, the heat in the air is absorbed by the refrigerant in the coil and the air is leaving the coil cooler.

    Air flow is designed so that maximum heat is absorbed keeping air throw far enough to cool the entire aria to be cooled.

    Therefore, Δt is not a fixed No. but will differ with certain situations.

  5. #5
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: delta T

    thanks chemi , sachin ,

    so delta T changes with different applications , so you couldnt just walk up to say an evap in a cold room , take delta t and work out if theres enough air flow?

  6. #6
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: delta T

    could anybody explain how we find out if theres sufficient air flow by checking delta T ? EG how does 2 temp readings tell you if theres correct airflow across an evap or condenser?
    thanks .
    If you know the rest of the data then yes.

    Transpose the formula Q=m x cp x p x dt for m

    i.e. m = Q / (cp x p x dt)

    m = volume
    cp = sh capacity
    p = density

    Only any good if you know Q and its 100% sensible load


    so delta T changes with different applications , so you couldnt just walk up to say an evap in a cold room , take delta t and work out if theres enough air flow? 07-07-2010 06:05 PM
    You can do a decent guesstimation
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  7. #7
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: delta T

    thanks thrash

    whats a good guesstimation ? or correct Delta T , how does these 2 temps tell you that you have correct airflow,
    Thanks for your time

  8. #8
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: delta T

    Consider this situation

    A split a/c unit running at full capacity (says 5kw on the nameplate)

    You measure air on at 23c and air off at 10c therefore dt =13k

    5/(13 x 1.205 x 1.005)

    5/ 15.73

    vol = 0.318 m3/s

    If this looks reasonable for the fan then OK

    Get a bit more accuracy by doing the condensor the same way.

    Or do it properly using anemometer/ balometer etc..
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  9. #9
    Join Date
    Jul 2007
    Location
    england
    Age
    44
    Posts
    98
    Rep Power
    17

    Re: delta T

    Arh thanks trash it's starting to make sense now.

Similar Threads

  1. Delta T at lower outdoor temperatures ?
    By JOSHUA NAGE in forum Technical Discussions
    Replies: 1
    Last Post: 10-05-2010, 06:35 PM
  2. Delta RA Capacities
    By Greengrocer in forum Air Conditioning
    Replies: 1
    Last Post: 23-10-2009, 05:14 PM
  3. Star delta
    By Deano240 in forum Fundamentals
    Replies: 8
    Last Post: 10-10-2009, 12:20 AM
  4. Replies: 2
    Last Post: 25-07-2008, 11:13 AM
  5. question on delta T values in air conditioning work
    By beachfronttech in forum Air Conditioning
    Replies: 2
    Last Post: 18-01-2008, 10:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •