    wendecai Guest

    Question About TEV



    Can anyone tell me what is the difference between TEV with MOP and TEV without MOP? What is MOP?Also i've install a new TEV onto the coldroom and the hissing sound was at the liquid line?I've check the pressure on low and high side.the charging looks fine.One strange thing was,only one pipe at the evaporator is icing up and it melts after few minutes.Is it that the orifice is too big which oversize?

    Pls Help??


    Thank you

    Jeff



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: About TEV

    Hi Jeff, have a read of this Sporlan document on TEVs, it details the MOP function.

    http://www.sporlanonline.com/10-9.pdf

    If you more or other stuff then make your choice..
    http://www.sporlanonline.com/literature.shtml
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: About TEV

    Quote Originally Posted by wendecai View Post
    Can anyone tell me what is the difference between TEV with MOP and TEV without MOP? What is MOP?Also i've install a new TEV onto the coldroom and the hissing sound was at the liquid line?I've check the pressure on low and high side.the charging looks fine.One strange thing was,only one pipe at the evaporator is icing up and it melts after few minutes.Is it that the orifice is too big which oversize?

    Pls Help??


    Thank you

    Jeff

    TEV Normal Thermostatic Expansion Valve.

    MOP Maximum Operating Pressure It will deliver refrigerant to a maximum pressure.

    The hissing you hear is refrigerant passing through the valve itself.

    Coolrunnings

    It is fundimentals of refrigeration.
    Did you change the valve like for like?
    Did you install an orifice and was it the same size as the one you took out?
    Did you pressure test and vac the system dry?

    Coolrunnings
    .
    Last edited by cool runings; 05-07-2010 at 10:39 PM.

  4. #4
    Join Date
    Mar 2005
    Location
    New Zealand
    Age
    43
    Posts
    64
    Rep Power
    20

    Re: About TEV

    It's simple really, an expansion valve has a charge of refrigerant in the bulb and carpillary, as the temp of the suction gas increases/decreases it raises/decreases the temp of the charge in the bulb which increases/decreases the pressure applied to the tx valve diaphram. In an MOP valve the charge of refigerant in the bulb is minimised so it can only increase in pressure to a certain point, once at that point even if more heat is applied it will not increase pressure on the valve diaphram so can not open the valve further. An example of where you would use an MOP valve would be a freezer with no CPR valve (crankcase pressure regulating valve). On a hot start or after a defrost where evaporating temperatures can be far too high for a low temp compressor the MOP valve will limit sution pressure protecting the compressor (but will make for a slow pull down). Hope this helps.
    Last edited by R. skiffington; 12-07-2010 at 10:51 AM.