    possible??



    hi,
    is it possible to have the right suction pressure but have excessive high superheat - enough to cause the compressor to overheat?



  2. #2
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: possible??

    wouldn't have thought so

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: possible??

    Who is to say what the right suction pressure is ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: possible??

    If you have high suction superheat the evap is being underfed with refrigerant or the system is picking up too much heat in the suction line.
    Its all about the temperatures, not so much the pressures, pressures only make sense when converted into temperature in a working system, its what the are designed to do, change the temperature in an enviroment.

    Give us some more info, system type, refrigerant, air on and air offs, pressures, superheats, subcooling and some of the clever people on here (not me ) will be able to tell you whats going on and where it going wrong.

  5. #5
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: possible??

    thanks
    not got alot but goin back tommorrow but heres what i have.
    cellar cooling evaportating at +5c onr407c
    temp at bulb for tev 22c room temp 22c
    evap coil only cooling at distributor,air on 22c air off 21c
    unit runs for 5 min then cuts out on overload , compressor hot cant touch it
    the compressor has just been changed and the customer informs me he has had at least 3 compressors in as many years
    just want a few ideas when i go back
    Last edited by sean1; 04-07-2010 at 11:39 PM.

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: possible??

    Quote Originally Posted by sean1 View Post
    thanks
    not got alot but goin back tommorrow but heres what i have.
    cellar cooling evaportating at +5c onr407c
    temp at bulb for tev 22c room temp 22c
    evap coil only cooling at distributor,air on 22c air off 21c
    unit runs for 5 min then cuts out on overload , compressor hot cant touch it
    the compressor has just been changed and the customer informs me he has had at least 3 compressors in as many years
    Suction pressure is to low for an air temp of 22C.
    Pretty bad state of affair.
    I bet the system is contaminated, wrong orifice or refrigerant charge, faulty TEV

  7. #7
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: possible??

    i was thinking faulty tev/orifice , what would you expect suction pressure to be or how would you calculate it?

  8. #8
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: possible??

    Quote Originally Posted by sean1 View Post
    i was thinking faulty tev/orifice , what would you expect suction pressure to be or how would you calculate it?
    You need to think of this in a different way.
    Get away from fixed figures.
    If this is a beer cellar, then the system would have been designed to run at 10C (well it was 20 years ago when I lived in the Uk).
    Your cellar is is at 22C (and is likely to have humidity), so this is under pull down load. So you would expect your suction pressure to be high, also a much higher head pressure (presume ambient is high, are you having a good summer) and a hottish liquid line.
    You would also expect higher superheat (load is likely to be higher than system capability)
    Electrical power draw will also be high (current)
    Think of your system as circle, you change one part, then the the rest will change.
    If you want to ckeck your superheat whilst the cellar is still hot, block of some of the air going through the evap. (I used to place beer cloths over the fan to restict flow) You should then see you SST and your SCT drop, then your valve will start to operate on the superheat.

  9. #9
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: possible??

    Quote Originally Posted by sean1 View Post
    thanks
    not got alot but goin back tommorrow but heres what i have.
    cellar cooling evaportating at +5c onr407c
    temp at bulb for tev 22c room temp 22c
    evap coil only cooling at distributor,air on 22c air off 21c
    unit runs for 5 min then cuts out on overload , compressor hot cant touch it
    the compressor has just been changed and the customer informs me he has had at least 3 compressors in as many years
    just want a few ideas when i go back

    You need to fit gauges to both suction and discharge...

    Is it condensing correctly??

    all the best

    coolrunnings

    .

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: possible??

    mad fridgie got it. In a commissioning phase, when the temperature on the secondary side are higher than expected, evaporating pressure AND superheating can be both high, or when evaporating pressure is ok (because of MOP TEV), superheating is excessively high.

  11. #11
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: possible??

    Only 1 degree c temp/diff across evaporator? Is the compressor semi or dome type and what is the discharge pressure and liquid temperature before compressor shutdown?