    Unhappy Overload protector



    I have Fedders F1FM109S6A (sold in Finland) air conditioner having a long time
    to reset if the overload protector has been trip. Is this normal?


    The O.L.P is Klixon MRA99018-12027 so if you have any specs, it would help a lot.

    If I replace it, how accurate are the specs? Can I just use any O.L.P for this size unit?
    Ferrers specs: cooling power: 2600 W, Current draw: 5.4 A, Electric power draw: 1180 W.

    What is the adjustment screw for? Can I adjust the triggering current or something?



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Overload protector

    Hi Gram-man,

    Is this one of those bi metalic klixons that mount externaly on the compressor? They will take a long time to reset as the compressor body has to cool down first.

    The question i would ask is why does it keep tripping, (unless faulty) it is the last hope the compressor has to survive being run outside of its design paramiters.

    Would be worth checking for high suction superheat, blocked condensers, poor electrical supply, faulty capacitors or relays etc, too frequent cycling on thermostat or pressure switches etc, or a faulty compressor.

    Jon

  3. #3
    Join Date
    Jul 2009
    Location
    Finland
    Age
    70
    Posts
    12
    Rep Power
    0

    Re: Overload protector

    Hi, Jon. Yes, it is assembled on the compressor under a plastic cover. It cuts the compressor off if you switch the conditioner off and off too quickly. So, I believe it is normal operation to protect the compressor. I believe that the compressor draws that much current it makes the OLP to trip when it is hot.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Overload protector

    How much current is the compressor pulling? and is it more than is on the data plate?

    Is this a low starting torque compressor? maybe the stat is turning back on too soon.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Overload protector

    Just take it off.
    These are not reliable parts. If it gets hot once and stop the compressor, the contacts are going bad.

    Instead use a proper size circuit breaker for the unit.

  6. #6
    Join Date
    Jul 2009
    Location
    Finland
    Age
    70
    Posts
    12
    Rep Power
    0

    Re: Overload protector

    Quote Originally Posted by chemi-cool View Post
    Just take it off.
    These are not reliable parts. If it gets hot once and stop the compressor, the contacts are going bad.

    Instead use a proper size circuit breaker for the unit.
    As a sertified professional I can't take it off because after that, the equipment is not in the original condition. It is forbidden in Europe to take any safety features off. If something happens, the insurance company may repudiate. The regulations are mandatory.

Similar Threads

  1. Inline surge protector
    By wilson77 in forum Air Conditioning
    Replies: 1
    Last Post: 20-11-2009, 12:58 AM
  2. Current Overload Trip
    By Meer Abdulrehma in forum Trouble Shooting
    Replies: 7
    Last Post: 19-10-2009, 03:29 PM
  3. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  4. thermal Overload
    By marc5180 in forum Trouble Shooting
    Replies: 51
    Last Post: 03-11-2007, 10:25 PM
  5. Setting Overload
    By Abe in forum Electrical
    Replies: 11
    Last Post: 06-01-2006, 01:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •