    Where to vent pressure relief?



    Hi all.
    I would like to know where the pressure relief lines are vented too on the plants you deal with, what works best and what regulations need to be complied with in your country.

    Most plants I have seen have the vent lines piped to the evaporative condenser air outlet so the NH3 would mix with the water saturated air. Not so good if the fans not running.

    Cheers



  2. #2
    Join Date
    Jun 2009
    Location
    Canada
    Age
    55
    Posts
    82
    Rep Power
    15

    Re: Where to vent pressure relief?

    Hi Superfridge

    It's pretty much he same here. Reliefs are piped to the roof, generally up past the condensers. One regulation we must follow in my part of the country is, end of relief stack must be 25 ft above roof level and 25 ft away from any opening into the building.

  3. #3
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Where to vent pressure relief?

    prv's should be vented to the outside using steel pipe work not sure on the regs for NH3

  4. #4
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Where to vent pressure relief?

    US from Expat Canadian:

    (2) model Constuction type codes concerned with what happens to neighbourhood should refrigerant be expelled; and national Design codes concerned with that and integrity of system....So they don't agree. And they are all subject to endorsement or rejection by the local jurisdiction having authority. And some jurisdictions adopt and retain old versions.

    Constuction type codes indicate: 10 Aborption tank (used to have to hold entire R-717 charge at 1 lb/gal concentration) but practicalities have decreased that to 1-hours discharge from your hgihest capacity SRV; 2) flare which required some good siting and an external fuel source and usually caused sour looks from the local fire prevention folks; 3) to atmosphere: largely per the ASHRAE 15 and the IIAR-2: a lot like Canadian Ice indicates though there are a couple of additional restraingts. It gets more rigoruus once you exceed a certain charge, because with PSM/RMP you have to go through plume modelling and consider location of (multiple) roof accesses and prevailing wind rollover and so on; basically to establish that a0 your own people can get out and b) the neighbouts and the fire fighters will survive....

    And none of that covers leak detetion, emergency ventilation, means of identification for the point of release, design of the discharge piping and so on.

  5. #5
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Where to vent pressure relief?

    Thanks for replys.
    It would appear "best practice" prevails with regards to the vent line release point.

  6. #6
    RG-NH3's Avatar
    RG-NH3 Guest

    Re: Where to vent pressure relief?

    Do you know the Constuction codes number that indicates 1 hour for discharge from your highest capacity SRV? or itīs only a practical rule. I need documentation about this issue.

  7. #7
    Join Date
    Dec 2010
    Location
    Oklahoma
    Age
    57
    Posts
    8
    Rep Power
    0

    Smile Re: Where to vent pressure relief?

    IMC 2009 code 1105.6.1 specifically states outdoors not less than 15 ft. Above the adjoining grade level and not less than 20 ft. From any window, ventilation opening or exit.

  8. #8
    Join Date
    Dec 2010
    Location
    Oklahoma
    Age
    57
    Posts
    8
    Rep Power
    0

    Smile Re: Where to vent pressure relief?

    I apologize my memory is slipping, it's IMC 2009 1105.7

  9. #9
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Where to vent pressure relief?

    Quote Originally Posted by CanadianIce View Post
    Hi Superfridge

    It's pretty much he same here. Reliefs are piped to the roof, generally up past the condensers. One regulation we must follow in my part of the country is, end of relief stack must be 25 ft above roof level and 25 ft away from any opening into the building.
    Same in Norway for land installations.

    On ships the rules say "406 A pipe with outlet opening at a position which is not considered dangerous for the ship or the surroundings of
    the ship, shall be led from the safety valve or the safety disc.
    If led to the atmosphere the outlet opening shall be protected against rain and snow and shall be fitted with a protection
    net made of corrosion resistant material to prevent ingress of foreign objects.
    When R717 is used as refrigerant the outlet shall be at a safe location as high as possible on the ship e.g. top of funnel
    or top of mast. The outlet shall be directed upwards.
    "
    -Cheers-

    Tycho

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Coldroom Air Pressure Relief Valves
    By CoolKids in forum Commercial
    Replies: 9
    Last Post: 25-07-2008, 07:46 AM
  3. High Deferential Oil Pressure Alarm
    By NNNNNN in forum Trouble Shooting
    Replies: 27
    Last Post: 24-12-2007, 01:06 PM
  4. over-under pressure relief valve
    By philip de moor in forum Industrial
    Replies: 3
    Last Post: 08-01-2004, 12:50 PM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •