    Unhappy 2 degree C cold room evaporator question.



    I have been looking after a friend cold room made by a company called Celltherm. A leak appeared about 12 months ago on the evaporator on the coil end right on the bend that I managed to repair. About 2 months ago a crack off of the original leak appeared and has gotten worse to the extent that I need to replace either the coil block or the complete evaporator.

    When speaking to Celltherm the unit is now defunct (made approx. 2000) and they have no spares.

    The unit says 3.39kw absorbed and 6.41kw cooling duty.
    The room measures (and this is where I become slightly confused) 2.8 meters by 1.4 meters and 1.95 high. So what I need to know is what size in kw evaporator do I need?? The product in the room is cheese, and the room is used to full capacity.

    The factory evap uses a capillery line, that I would like to retain in order to keep costs down (mates rates).

    The factory unit measures 250mm x 315mm x 250mm. Is that big enough for a 6kw cooloing capacity??!

    I was thinking the room is rated at more like 2-3kw?

    Thanks in advance.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: 2 degree C cold room evaporator question.

    For cheese you need dedicated evaporator to avoid leaks (corrosion) on evaporator coil.
    What is original evaporator make and model#?

  3. #3
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    425
    Rep Power
    20

    Re: 2 degree C cold room evaporator question.

    Your mate is fortunate to have had so many years service from that coil. The modern copper coils are so thin. I've seen them rot out in a couple of months when used for cheese storage.

    Andy

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: 2 degree C cold room evaporator question.

    hi
    I would stick to the same size u have
    But order a new evaporator either aluminum aluminum, or copper with special coating for corosive areas
    Good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Feb 2005
    Location
    UK
    Age
    44
    Posts
    13
    Rep Power
    0

    Re: 2 degree C cold room evaporator question.

    Really?! Wow I never knew that, it's a celltherm module split type unit cell box 2 model number asn075xmje serial number 57249. Apparantly that celltherm went bust which is why the spares are no longer avaliable.

    So storing cheese is a real problem? is it because of the way it breathes? I'm a chiller engineer so cold rooms are new, we this aspect anyway.

  6. #6
    jeycon's Avatar
    jeycon Guest

    Re: 2 degree C cold room evaporator question.

    Celltherm Coldrooms are still very much in business and still based in Narborough, Leicester!

Similar Threads

  1. Insulation for Cold Room
    By tjk2007 in forum Fundamentals
    Replies: 25
    Last Post: 19-03-2010, 03:54 AM
  2. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 02:49 AM
  3. Cold room floor
    By Andy AC in forum Commercial
    Replies: 8
    Last Post: 19-02-2009, 05:26 PM
  4. LG Capacitor - Room not cold
    By kelamel in forum Trouble Shooting
    Replies: 8
    Last Post: 21-10-2006, 10:50 AM
  5. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 10:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •