    If any wise owl can shed some light on this. got a 8ft roll in milk not cooling. high superheat 24k. only tubes after distributor frosting. .has a eev valve with danfoss orifice no. 6 . have changed valve and orifice and filter stil high superheat.evap coil only frosts when evap fans switched off.Im thinking it could be logged with oil or distributor blocked any advice.by the way pack pressures are 220hp and 42 lp and on 404a



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: high superheat no cooling any advice??

    You say EEV! Than you say orifice. What is valve make and model #. EEV has electronic driver which control his working.

  3. #3
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: high superheat no cooling any advice??

    if the controller is a danfoss you need to make sure the coil of the eev says akv only or it wont work!

  4. #4
    Join Date
    Dec 2007
    Location
    london
    Posts
    6
    Rep Power
    0

    Re: high superheat no cooling any advice??

    I figured it out .Yes it is a akv with a number 6 orifice .what a strange set up. a roll in milk with a high superheat and only frosted tubes just after the distributor.46 suction pressure and 220 head reciever full and sight glass clear .Shut down all other cases to get maximum liquid to my trouble some case and still no luck.fitted cardboard to rule out ambient temperature but still no difference .blew out valave with nitrogen still no difference .And then it came to me .i changed the pack drier and my roll in milk shot down to temperature WHAAAT A BEAUUUUTY!!!!!

    Thanks for youre help

Similar Threads

  1. Refrigeration 101
    By Gary in forum Fundamentals
    Replies: 201
    Last Post: 01-11-2011, 10:18 PM
  2. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  3. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  4. How do you calculate Superheat?
    By zolar1 in forum Training
    Replies: 39
    Last Post: 10-05-2002, 02:37 AM
  5. lab scale cooling of a high shear mixer
    By Keith_99 in forum Industrial
    Replies: 10
    Last Post: 17-01-2002, 08:37 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •