    Scroll compressors



    Hi all

    Scroll compressors no brazing easy to change!!!!!

    Any one got any tips for getting the sight glass off apart from heating it.

    Regards bernard



  2. #2
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Scroll compressors

    Hi

    The king can take a pawn and no one will notice,a pawn can take the king and every one will notice.

    Even the mighty fall sometimes never under estimate the pawn.

    Regards Bernard

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Scroll compressors

    [QUOTE=bernard].. Scroll compressors no brazing easy to change!!!!! Any one got any tips for getting the sight glass off apart from heating it.
    QUOTE]
    English is not my mother-tongue but what do you mean with your 1st sentence? No brazing? Easy to change?
    Which sight-glass, oil sight glass on compressor, liquid sight glass?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Scroll compressors

    Hi peter


    Sorry I ment the oil sight glass,Its put in with some thread lock,if you put to much pressure on it,it shatters the glass.Was just enquiring if anyone had other techniques for removing it.

    regards bernard

  5. #5
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Scroll compressors

    Thanks will try that I guess its around 30mm.

    The king rarely moves and relies on the pieces around him for his strength but is there at the end.

    A pawn moves and is normally sacrificed,but has lived life at the sharp end.

    Regards Bernard

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Scroll compressors

    Hi Bernard,

    I'm a bit puzzled,
    Why do you want to take the sight glass off??

    Chemi

  7. #7
    Join Date
    May 2004
    Location
    southern england
    Age
    69
    Posts
    86
    Rep Power
    20

    Wink Re: Scroll compressors

    3rd party oil management systems require the bulls eye to be replaced with a hall effect sensor housing / adaptor plate. Thats why.

    Leave the rubber bungs in the discharge and suction. Lay the compressor on its side with sight glass upper most. Use a socket with an extension to undo, carefully as there should be a slight ofn pressure. Fit replacement oil management system, stand compressor upright and fit as mormal.
    it's only a fridge, fix it. ;)

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Scroll compressors

    Thanks,
    I'm surprised, the manufacturers did not prepared a connection for it.

    On the semi hermetic its ready for it and on Maneurop.

    Well, not a dull moment.

    Chemi

  9. #9
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Scroll compressors

    Hi

    What problems would occur if a liquid injection system on a scroll was permanently injecting.

    Thanks bernard

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Scroll compressors

    What problems would occur if a liquid injection system on a scroll was permanently injecting.
    You would end up losing the compressor. Liquid injection is used for compressor cooling primarily, although it can be used for other reasons such as pressure equalisation. If the compressor is not hot enough to vapourise the liquid as it is injected then you can end up with liquid slugging and a loss of lubrication leading to premature failure.

  11. #11
    Join Date
    May 2004
    Location
    southern england
    Age
    69
    Posts
    86
    Rep Power
    20

    Wink Re: Scroll compressors

    Quote Originally Posted by bernard
    Hi

    What problems would occur if a liquid injection system on a scroll was permanently injecting.

    Thanks bernard
    If the compressor was in a stationary condition the crankcase would fill with liquid. This would cause oil dilution on start up and possible long term damage. If the compressor is running then there are two types of liquid injection, a) the external pot which requires braizing, this contains a capillerie tube. b) is a thermostatically controled inlet valve which would shut off when the discharge is cool enough. Neither would experince problems if over cooling during run cycle.
    it's only a fridge, fix it. ;)

  12. #12
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Scroll compressors

    What problems would occur if a liquid injection system on a scroll was permanently injecting.
    Interesting you should ask, Bernard. We have a situation with parallel compressors where a former factory field service engineer and others decided that medium temperature liquid injection with R22 was actually causing liquid carryover into the separator, thus recycling unevaporated liquid with diluted oil - so the injectors were removed. Now, we are being asked to re-instate them. This situation differs from what you describe as "permanently injecting." However, the normal setup for these injectors is to inject regardless of discharge temperature, and always when the compressor is running. If injecting when the compressor is not running, Chillyhamster put the likely outcome in fair words.

    The injectors I am being asked to reinstate are the canisters that have the capillary tube wound up in them, operated by a solenoid in parallel with the compressor contactor. Chillyhamster, is there another Copeland approved method of liquid injection? You mention a thermostatically controlled device?

  13. #13
    Join Date
    May 2004
    Location
    southern england
    Age
    69
    Posts
    86
    Rep Power
    20

    Wink Re: Scroll compressors

    Hi Dan, DTC can only be fitted to scroll comp designed for it ( hole in top center, covered with plastic plug) where temp sensor is fitted. Unit is attached to the same injection port as the cap can. cap can can be fitted in lou of the DTC. seems like i have been to the moulin rouge with all these can cans.
    it's only a fridge, fix it. ;)

Similar Threads

  1. Hitachi scroll compressors
    By tonydeith in forum Commercial
    Replies: 3
    Last Post: 21-01-2011, 01:48 PM
  2. crank case heaters in scroll compressors
    By abbasi in forum Fundamentals
    Replies: 19
    Last Post: 03-08-2010, 03:04 AM
  3. Danfoss parellel scroll compressors
    By Lc_shi in forum Technical Discussions
    Replies: 2
    Last Post: 30-03-2006, 08:20 AM
  4. scroll compressors
    By bernard in forum Supermarket Refrigeration
    Replies: 16
    Last Post: 16-09-2004, 08:31 PM
  5. Scroll compressors
    By Dan in forum Trouble Shooting
    Replies: 14
    Last Post: 29-11-2002, 04:06 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •