Thread: evaporator ice
30-06-2010, 10:00 AM #1
evaporator ice
the problem is ice on evaporator
now the caz is (1) sorthage of refregerant.
(2) system choking?
or any other reasion.
30-06-2010, 03:15 PM #2
30-06-2010, 10:10 PM #3
Re: evaporator ice
I should go for moisture around the coil which is below freezing temperature of water ,...just a wild guess..
01-07-2010, 05:46 AM #4
Re: evaporator ice
no there is no any deforst system in the said ac.
01-07-2010, 06:50 AM #5
Re: evaporator ice
What was the presuures? also Check up the evap. filter cleanliness and fan speed.
01-07-2010, 07:16 AM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: evaporator ice
Problem is your description of problem. Not enough data.
Now after 3 post we found that is air conditioner in qustion here.
Describe your unit with model# and describe conditions around unit and its placemant.
Also:
Here is a list of the temps/pressures needed to troubleshoot a system:
Evap air/water in temp
Evap air/water out temp
Low side pressure or saturation temp
Suction line temp at evap outlet
Suction line temp at compressor inlet
Cond air/water in temp
Cond air/water out temp
High side pressure or saturation temp
Liquid line temp at receiver or condenser outlet
Liquid line temp at TXV inlet
The more information provided the more accurate the diagnosis.