    evaporator ice



    the problem is ice on evaporator

    now the caz is (1) sorthage of refregerant.

    (2) system choking?

    or any other reasion.



  2. #2
    Join Date
    Nov 2009
    Location
    canada
    Age
    51
    Posts
    64
    Rep Power
    15

    Re: evaporator ice

    Quote Originally Posted by mianrizwan View Post
    the problem is ice on evaporator

    now the caz is (1) sorthage of refregerant.

    (2) system choking?

    or any other reasion.

    To short of defrost or not defrosting enough.
    evap is close to entrance point with warm air going up and icing it

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: evaporator ice

    I should go for moisture around the coil which is below freezing temperature of water ,...just a wild guess..
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Mar 2010
    Location
    pakistan
    Posts
    44
    Rep Power
    0

    Re: evaporator ice

    no there is no any deforst system in the said ac.

  5. #5
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: evaporator ice

    What was the presuures? also Check up the evap. filter cleanliness and fan speed.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: evaporator ice

    Quote Originally Posted by mianrizwan View Post
    the problem is ice on evaporator

    .
    Problem is your description of problem. Not enough data.
    Now after 3 post we found that is air conditioner in qustion here.
    Describe your unit with model# and describe conditions around unit and its placemant.
    Also:
    Here is a list of the temps/pressures needed to troubleshoot a system:

    Evap air/water in temp
    Evap air/water out temp
    Low side pressure or saturation temp
    Suction line temp at evap outlet
    Suction line temp at compressor inlet

    Cond air/water in temp
    Cond air/water out temp
    High side pressure or saturation temp
    Liquid line temp at receiver or condenser outlet
    Liquid line temp at TXV inlet
    The more information provided the more accurate the diagnosis.