    humidifier problem



    hey guys
    got a problem with a humidifier on a crac unit in a data centre.System keeps displaying low current alarm for humidifier.humidifier contactor is coming on when required i have correct voltage also, yet bottle does not pull correct current.Bottle is filling correctly have tried changing bottle,drain solenoid incase water was escaping and have even tried putting a touch of salt in the bottle to bring it to life
    any idea guys what my problem is because this unit is doing my head in
    thanks brad



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: humidifier problem

    hi tradybrad, try some salt in the water, the amps should jump up, then it will dump some water< cos there will be too much conductive elements in the hum bottle , then you got to set either the dump setting , or the amp setting, all the best, sedgy
    Last edited by sedgy; 30-06-2010 at 03:52 PM. Reason: yes your right - bad spelling

  3. #3
    Join Date
    Nov 2008
    Location
    australia
    Posts
    17
    Rep Power
    0

    Re: humidifier problem

    hey m8 whats controlling the contactor? might be a parrameter in controller to increase water conductivity threshold?

  4. #4
    Join Date
    Jan 2010
    Location
    australia
    Age
    39
    Posts
    32
    Rep Power
    0

    Re: humidifier problem

    thanks for the reply guys i looked into this problem further found humidifier water feed had inline filter cartridges that were no good affecting the water quality going to the bottle
    i have removed cartridge for now to see how system performs so far so good though no alarms will keep you posted
    brad
    ozziebill thanks for the heads up about the threshold will definatly check that out also.

Similar Threads

  1. MFI AMP6855 defrost problem
    By gliderpilot47 in forum Domestic
    Replies: 4
    Last Post: 12-01-2011, 12:11 PM
  2. problem with GE air con power problem
    By Richie101 in forum Air Conditioning
    Replies: 6
    Last Post: 05-11-2009, 04:00 PM
  3. Samsung Vivace Problem AQV24VBCN
    By goldpau in forum Air Conditioning
    Replies: 0
    Last Post: 18-09-2009, 06:28 PM
  4. Saunier Duval Problem
    By mallorcanangel in forum Air Conditioning
    Replies: 1
    Last Post: 10-07-2009, 01:26 AM
  5. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •