    Chiller to AHU Pressure Problem



    hi Friends.
    i have pblm with my chiller to ahu Pressure
    My Chiller Standing at 3rd floor CHWS 50 Psi Pressure. my ahu standing at basement floor.
    actual way chilled water supply Psi + Gravity needed to b.f ahu return, but i am getting only 15 psi what is the pblm?. Please Help me..................



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Chiller to AHU Pressure Problem

    1st problem, you are writing in shorthand, makes it hard to read and understand.

    Loss of pressure could be due to:-

    Is the pipe sizing correct?
    Is the pump running?
    Is the pump rotation correct?
    Are all of the valves open?
    Is the water clean?
    Are there any blockages in the system?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    15

    Re: Chiller to AHU Pressure Problem

    Quote Originally Posted by bibin777 View Post
    hi Friends.
    i have pblm with my chiller to ahu Pressure
    My Chiller Standing at 3rd floor CHWS 50 Psi Pressure. my ahu standing at basement floor.
    actual way chilled water supply Psi + Gravity needed to b.f ahu return, but i am getting only 15 psi what is the pblm?. Please Help me..................
    Measure AHU inlet and outlet pressure then it clear U what going on inside of the AHU cooling coil.
    Then look at others option......

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Chiller to AHU Pressure Problem

    You will always get system losses.

    I would be more concerned if the flow rates weren't correct as this would lead to a loss of duty

  5. #5
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Chiller to AHU Pressure Problem

    is this a new plant or an old one that has this trouble for the first time.

    some more history will help us to understand the situation, and will give better possible solutions for youre problem.

    Ice

  6. #6
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: Chiller to AHU Pressure Problem

    hello dear
    you check ur waterpump inlet strainer. all valves.

Similar Threads

  1. Chiller connectivity problem
    By ALLAHHOOPK in forum New Technologies
    Replies: 2
    Last Post: 12-05-2009, 05:57 PM
  2. Chiller tripping Problem
    By bhasadu in forum Trouble Shooting
    Replies: 0
    Last Post: 21-06-2008, 09:12 AM
  3. R11 Centrifugal Chiller Oil Problem
    By iceman007 in forum Trouble Shooting
    Replies: 8
    Last Post: 17-02-2008, 02:14 AM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •