    Oil Temperature -Trane Chiller



    Dear all

    We are having Centrifugal Water Chiller of Trane using HCFC -123 as the refrigerant . We are facing a problem with the Oil Heater. The temp is not raising above 90 F it should be above 140 F.We tried replacing the heater but still didnt worked , Checked the thermowell .Everything is working fine except the Oil temp . What could be the possible reason for this



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Oil Temperature -Trane Chiller

    I had a similar problem on an older carrier centrif - it turned out to be the thermostat.

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Oil Temperature -Trane Chiller

    hi u should check the settings of the controller.it might be set to low!!!as said before.
    and make sure when unit is stopped that there is no water flow through the condenser.
    good luck
    Last edited by goshen; 01-07-2010 at 05:16 PM.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Trane chiller Training
    By sefuss in forum Training
    Replies: 0
    Last Post: 26-05-2010, 05:01 PM
  2. Trane chiller HP fault
    By Kirky in forum Air Conditioning
    Replies: 7
    Last Post: 19-05-2010, 08:39 PM
  3. Trane chiller problem
    By dannycool in forum Air Conditioning
    Replies: 6
    Last Post: 08-04-2010, 11:31 PM
  4. NVQ 3 online test
    By Burrah Boy in forum Training
    Replies: 7
    Last Post: 28-10-2009, 08:35 PM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •