Cost of Removing Extra Heat in Summer
> + say you have a house
> + it has a normal AC
> + it;s 90 degrees outside
> + normal roof, insulation etc
> + say the house is 2400 sq feet, it has a 4 ton central
> air
> + inside temp is set at 75F
> + normal sunshine
> +
> + here is the question:
> + how much extra AC cost is it if you add a 100 watt heat
> source in
> + the house?
> +
> + state other conditions or assumptions to reach the answer
yes i know there are a lot of variables
just a ball park answer
maybe just something like
"if the AC is SEER 15, it is 50% efficient, so it will cost 200 watts to get 100 watts of heat out"
thx
wle
-
29-06-2010, 05:17 PM #2
Re: Cost of Removing Extra Heat in Summer
Simpler to just tell the kids to turn the lights off, or if they insist on leaving them on put in smaller bulbs
-
29-06-2010, 11:14 PM #3
Re: Cost of Removing Extra Heat in Summer
College question is it?
Seems to be second copy email.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
30-06-2010, 12:41 AM #4
-
30-06-2010, 01:47 AM #5
-
30-06-2010, 01:48 AM #6
Re: Cost of Removing Extra Heat in Summer
is it really that hard to figure out?
wle
-
30-06-2010, 10:53 AM #7
-
30-06-2010, 03:29 PM #8
Re: Cost of Removing Extra Heat in Summer
A continuous 100 watt source operating in a conditioned space for one month (720 hours) will add a total of 72 KW to the space. 72 KW us equivalent to 246 Btuh. If the SEER if 15, the AC can remove 15 Btuh for every Watt of power expended. Therefore, watts expended on a hot day will be 246/15 or 16 KW. If the cost of power is 10 cents per KWh, the cost to run a 100 watt source for a month will be $1.60 USD.
A tutorial: EER (and SEER) = Btuh of heat removed /watts expended. One watt = 3.413 Btuh, so EER = (Watts removed x 3.413)/ (watts input to the ac unit). Finally, 72 KW is equivalent to 246 Btuh. Hence, an EER of 15 can be 246 Btuh/16 KW.
Note that the energy used, KWh, is independent of the time taken to remove the heat. If the entire 72 KW is removed in 1 hour, the energy used is 16 KWh. If, as in the example, it is removed at the rate of 100 Watts each hour for 720 hours, the energy used is still 16 KWh.
Note also that the size of the house
and ac unit are irrelevant. The only relevance to the outdoor temperature is that this would be summer, and the system is always in cooling mode, trying to maintain a set temperature.
-
30-06-2010, 09:41 PM #9
Re: Cost of Removing Extra Heat in Summer
good answer!!!
THANKS
WLE
-
01-07-2010, 02:28 PM #10
Re: Cost of Removing Extra Heat in Summer
Hello, your answer is very nice which is based on some technical calculation.
It is very helping for the community , in fact air conditioning should be dealt with extra care.
-
04-07-2010, 03:21 AM #11
Re: Cost of Removing Extra Heat in Summer
I guess this is splitting hairs since the example is an incandescent lamp, but does 100 watts in really equal 100 watts out? Of the 100 watts of input, "only" about 98 of those watts are released directly as heat, while the remaining two are visible light. Now, I guess those two watts of light do break down (such as it is) into heating the surfaces they illuminate, though in any typical scenario some light is lost out the window, thus the load on the A/C would be very slightly less than 100 watts.
I suppose the same could be said of motors, in that the motion breaks down to heat through friction. Still, if you were able to do this exercise in a completely controlled environment, would you find that ALL the work done by all electrical or electromechanical devices eventually degenerates to an equal amount of heat as the device's input power? Something tells me this isn't the case, even if the actual amount of work that doesn't degenerate to heat is very very small.
Similar Threads
-
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Heat Reclaim
By chilled2005 in forum Supermarket RefrigerationReplies: 19Last Post: 05-05-2008, 05:32 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
heat pump capacity adjust
By Lc_shi in forum FundamentalsReplies: 5Last Post: 14-02-2006, 07:32 AM -
R134a <-> liquid heat exchanger design
By DaBit in forum Technical SpeculationsReplies: 19Last Post: 10-05-2002, 08:36 AM