    SYRIA
    44
    11
    high oil differential pressure
    i have a problem in two air cooled chillers single screw compressor , two units ( 4 circuit ) trip at same alarm high oil differential pressure after ( 10 - 30 ) minuties
    note : units are new ( under start up )
    i hope to find help on site or manual by Email
    waseem
    waseemnaamo@yahoo.com
    38
    Re: high oil differential pressure
    Hi waseem,
    You have not included the type of unit or manufacture.
    But would suggest from limited information that the oil filters need replacing. Generally high differential limits are protecting the compressor from lack of lubrication.
    magoo
    Dec 2006
    Iran
    43
    55
    Dear freind,
    this problem might be cause of some diffrent items:
    1) if you have plc control of the diffrential oil pressure check the alarm setpoint first and change it to maximum.
    2) check the pressure sensors and be asured that they works correctly and calibrate.
    3) check the oil type you are using.it must approved by manufacture.
    4)check oil pipe and pass in compressor body and filter situation.
    5) if all of above steps passed and problem remaind please replace the oil filter
    Best regard