    condensate drainage problems



    hello gents, got a ahu thats leaking condensate, this is the situation. condensate from the evap coil wont run down condensate drain line because the supply air fans seems to be pulling on this water and by intrainment depositing it further along the duct work where there is no drainage and so it leaks where it can. what i find is if i turn the supply air fans off water drains quite freely down the condensate drain or the same thing happens if i open the filter asscess hatch down stream of the evap coil. note the problem is not the condensate drainage pipe work. any help would be great.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: condensate drainage problems

    Is it a U trap? Maybe its not low enough?

    Are the filters clean? Any return air obstruction?

    Was it like that from the beginning or is it new problem?

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: condensate drainage problems

    Few things to check,

    Is the coil clean?

    As chemi-cool said is the u trap correct?

    On the return air ductwork Is there anything else tee'd in to it?

    I had this a few weeks back in a restaurant and found they had tee'd into the return ductwork a kitchen dishwasher.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: condensate drainage problems

    you need to fit a p trap and fill it with water

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: condensate drainage problems

    I think if the drain pan is on the sucky side of the fan it needs a p trap (which will need priming), if its on the blowy side it doesn't want one.

  6. #6
    Join Date
    Dec 2007
    Location
    n.ireland
    Age
    45
    Posts
    38
    Rep Power
    0

    Re: condensate drainage problems

    had something like this 2day,ended up the filters were plugged solid and that created a vacum inside the unit,causing the water 2 splash round with the fans goin. replaced the filter mesh and that sorted the problem..

  7. #7
    Join Date
    Jun 2010
    Location
    Wales
    Posts
    45
    Rep Power
    0

    Re: condensate drainage problems

    Quote Originally Posted by aircool View Post
    had something like this 2day,ended up the filters were plugged solid and that created a vacum inside the unit,causing the water 2 splash round with the fans goin. replaced the filter mesh and that sorted the problem..
    Yep if the filter is chocked up, it will cause a vacum the other side of the filter which is all the coil etc, make sure the filter is clean and again check the U trap is in the correct position, it does matter!

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: condensate drainage problems

    Also make sure that the trap is full of water otherwise it will never work.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2003
    Location
    london
    Posts
    26
    Rep Power
    0

    Re: condensate drainage problems

    thanks for all the responses, the traps and filters are all ok, what i find when system operating is the condensate water in the condensate pan is pulled by the suction of the supply fans to such a degree that the water is kept away from the drainage pipe almost lifted out of the tray. when an access panel is opened up stream then the water flows down the trap quite freely.

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: condensate drainage problems

    Your trap on the drainage line should be close to the drain pan and at least 150mm deep then the drain should fall away from the trap. If you have a large static pressure on the fan the drain line may need to be larger than 20mm diameter

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: condensate drainage problems

    Quote Originally Posted by mr saw View Post
    thanks for all the responses, the traps and filters are all ok, what i find when system operating is the condensate water in the condensate pan is pulled by the suction of the supply fans to such a degree that the water is kept away from the drainage pipe almost lifted out of the tray. when an access panel is opened up stream then the water flows down the trap quite freely.
    You say that traps are OK but they don't seem to be working.

    Check the static pressure at the trap inlet and ensure that the trap is deep enough.

    Something on the inlet side of the fan is blocked to have increased the suction pressure from what, we assume, was a working drainage system.

    Blocked filter, collapsed filter, dirty coil, fire damper dropped, inlet grille damper closed etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Apr 2003
    Location
    london
    Posts
    26
    Rep Power
    0

    Re: condensate drainage problems

    the evaporator coil did have a carpet layer of dirt which has been clean, thinking about it the coil would really need a deep clean because internally it is still floud to a degree. thanks chaps...

  13. #13
    Join Date
    May 2006
    Location
    Sussex
    Posts
    364
    Rep Power
    20

    Re: condensate drainage problems

    The Fresh air intake louver will normally have a bird wire screen behind it, which can get clogged up after a while. Maintenance deals with filters but can miss this one.

    Might be worth a check if all else looks okay on the suction side of fan.

Similar Threads

  1. Carrier 30XA Liquid chiller Problems
    By Ed Burris in forum Commercial
    Replies: 7
    Last Post: 13-08-2010, 08:12 PM
  2. Condensate drainage regulations
    By topfridgeman in forum Technical Discussions
    Replies: 1
    Last Post: 05-03-2009, 12:12 AM
  3. Hartell Condensate Pump
    By Grizzly in forum Air Conditioning
    Replies: 8
    Last Post: 03-01-2008, 10:08 AM
  4. Replies: 10
    Last Post: 18-03-2006, 08:35 PM
  5. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •