    Payne HP



    I have a Heat Pump that will kick off on high pressure even after the coils were cleaned any advice? This is a packaged unit 2 1/2 ton.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Payne HP

    Airflow, fan running correct way, blade fitted right way round and correct blade for unit, unit overcharged, or non condesables in system. Faulty hp switch.
    Restricted discharge pipework or stuck reversing valve.

    Think if you were trying to make something go out on hp, how would you do it? then check through the most likely to the least likely.

    Jon

  3. #3
    Join Date
    May 2010
    Location
    Charleston, WV
    Posts
    13
    Rep Power
    0

    Re: Payne HP

    I was thinking reversing valve since unit is not too old fan and everything is original hp switch is ok gauges say too high

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Payne HP

    If you can check the pressure either side of the rv then you will know for sure.

    Have you tried it in heating and cooling mode? And does it trip in both modes?

  5. #5
    Join Date
    May 2010
    Location
    Charleston, WV
    Posts
    13
    Rep Power
    0

    Re: Payne HP

    Not yet I've recovered refrigerant in order to dehydrate and straightened some coil fins but I have to run some power to unit. I bought it for 300 dollars and figured if I had to change rv it would still be a good buy only about 3 or 4 years old