    Daikin Super Inverter works like on/off control



    Daikin Air conditioner Ducted
    Outdoor unit: RZP145DVI
    Indoor unit: FDYP145DFVI
    Control unit: BRC1C61

    In spite of this being an inverter system, it works more like an on/off control system when heating. This results in cold air being blown when set point is reached. I expected it to blow warm air once the rooms had stabilized, but, alas, it doesn't. This is why I bought and paid a lot more for an inverter. Joke!
    Therefore I want to program it to turn off the indoor fan when temperature set point is reached.
    Does anyone know the input codes to the BRC1C61 control unit to do this - it can be done. Thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin Super Inverter works like on/off control

    Email sent.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin Super Inverter works like on/off control

    Quote Originally Posted by 66sixty66six66 View Post
    Daikin Air conditioner Ducted
    Outdoor unit: RZP145DVI
    Indoor unit: FDYP145DFVI
    Control unit: BRC1C61

    In spite of this being an inverter system, it works more like an on/off control system when heating. This results in cold air being blown when set point is reached. I expected it to blow warm air once the rooms had stabilized, but, alas, it doesn't. This is why I bought and paid a lot more for an inverter. Joke!
    Therefore I want to program it to turn off the indoor fan when temperature set point is reached.
    Does anyone know the input codes to the BRC1C61 control unit to do this - it can be done. Thanks.
    Hi,

    Continual on/off could be due to;

    Unit capacity over sized for the application.
    Return air sensor being influenced by fresh air/discharge air.
    Poor set up/commissioning.

    Also the indoor unit fan should enter low low fan speed when thermo off in heating mode.
    Last edited by VRVIII; 28-06-2010 at 08:36 PM.

  4. #4
    66sixty66six66's Avatar
    66sixty66six66 Guest

    Re: Daikin Super Inverter works like on/off control

    Quote Originally Posted by VRVIII View Post
    Hi,

    Continual on/off could be due to;

    Unit capacity over sized for the application.
    Return air sensor being influenced by fresh air/discharge air.
    Poor set up/commissioning.

    Also the indoor unit fan should enter low low fan speed when thermo off in heating mode.
    Thank you VRVIII for your comments. I think all three suggestions could be a factor. We normally run it on Low fan speed. It would be nice if the indoor fan speed would reduce even further as the room stabilizes. Regards, Gavin

  5. #5
    Join Date
    Dec 2006
    Location
    Aust
    Posts
    68
    Rep Power
    18

    Re: Daikin Super Inverter works like on/off control

    May be a capacity issue (Oversized).
    Better if sized ok to run on high fan.
    You will not get the rated capacity out of the machine on low fan. Low fan you will not acheive the rated airflows.
    The unit is trying to maintain target indoor coil temp. Put in on low and the coil temp will increase causing the outdoor unit to ramp down. This will cause the outdoor to ice faster and create more defrosts. You can cycle fan however this will do both for Heat and cool. Also you have the 6 min air sampling which may be a problem for you.
    Heat statification may be an issue also.

    A remote sensor may help you out but you need to know the cause of your problems. Remote sensor will help with defrost if you are initiating defrost due to deminished capacity (return air not rising in help) but doesnt look like to problem you are facing.

    Sound more like a setup or install issue rather then a unit problem.

    Keep in mind if unit is zoned this can also effect temp control based on how zones are set up.

    When unit cycles off on heat unit goes to LL fan. This is usally o.k for 90% of installs hower grille selection and house design can cause this to be a problem.

    Hope the code sort out your issue

Similar Threads

  1. Daikin inverter vrv on R22
    By sexysouthwest in forum Air Conditioning
    Replies: 5
    Last Post: 29-06-2011, 10:14 PM
  2. Daikin VRF inverter scroll compressor
    By Cofreth in forum Technical Discussions
    Replies: 2
    Last Post: 09-11-2009, 10:04 PM
  3. daikin vrv on/off remote signal trouble
    By coriolan in forum Air Conditioning
    Replies: 7
    Last Post: 09-06-2007, 11:27 AM
  4. PIR Control for a Daikin
    By daddymac in forum Air Conditioning
    Replies: 3
    Last Post: 11-05-2007, 07:29 AM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •