Thread: Lennox chiller Re-wire
-
24-06-2010, 09:02 PM #1
Lennox chiller Re-wire
Some technical help needed on this one folks
i have a lennox wa370 water chiller on site using 6 copeland scroll compressors with tev's the control pcb's were destroyed by a dodgy tech so i have the task of rewiring the chiller using mechanical controlls as the parts from lennox are over priced and a too long of a lead time, also the client wants the chiller running asap regardless of cost.
so far i have fitted a carel Ir32 control for the compressors and fan speed control for the fans with flow and hp-lp switches wired in series the chiller runs fine with regards to temperatures the problem i have is the control is constantly starting and stopping the compressors when they near setpoint i have tried various setting in the controls to prevent this diff dead bands etc so what i need to do is fit anti recycle timers having trawled the rs website i can't seem to find one suitable i need a 24v timer with a minimun of 15mins restar time if anyone can recomend a timer to use i would be very gratefull
Thanks in advance
-
24-06-2010, 11:04 PM #2
Re: Lennox chiller Re-wire
RS are the people you need but you can get an ON-DELAY timer from most good electrical wholesalers.
You need function type 111, as here
http://uk.rs-online.com/web/generalD...?id=info/timer
Something like this ?
http://uk.rs-online.com/web/search/s...duct&R=0214640Brian - Newton Abbot, Devon, UK
Retired March 2015
-
25-06-2010, 05:47 PM #3
Re: Lennox chiller Re-wire
cheers Brian i got some boyce control m1mft's they did the job chiller runs better now than it ever did with lennox controls
-
25-06-2010, 10:18 PM #4
Re: Lennox chiller Re-wire
Well done, some decent job satisfaction in this one I expect.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-06-2010, 04:19 AM #5
Re: Lennox chiller Re-wire
if you used the IR32 model carel it has multiple outputs, you can have minimum on and off times for each output. C8 is the minimum off time of the same output, C9 is the minimum on time of the same output, cheers Paul
-
29-06-2010, 05:38 PM #6
Re: Lennox chiller Re-wire
-
30-06-2010, 05:37 AM #7
Re: Lennox chiller Re-wire
To explain the carels use this
First two letters
IR= Infra red programmable
Second two numbers
32= old series
33= new series
third letter
V= 1 output
W=2 outputs
Z= 4 outputs
Fourth number
0=NTC temp input
1=PT100 temp input
2=Thermocouple input J/K
3=4/20mA input
So an IR32Z3 will take a 4/20mA input say from a pressure transducer and has 4 digital outputs for say start comp and 3 stages of loading
cheers Paul
-
07-07-2010, 04:47 PM #8
Re: Lennox chiller Re-wire
Thanks for the info paul i fitted two controlers to the unit it's been running nicely ever since (fingers crossed)
Similar Threads
-
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
Problems in r22 chiller design
By umeshpradhan in forum Technical DiscussionsReplies: 9Last Post: 06-07-2010, 10:39 AM -
lennox chiller fault code
By redroge in forum Trouble ShootingReplies: 1Last Post: 03-02-2010, 07:09 PM -
Absorption Chiller VS Mech. Chiller
By Intern in forum IndustrialReplies: 20Last Post: 30-05-2009, 08:31 AM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM