    3 systems, R22 +R417a -- Pressures look okay?



    Hi there.
    Could someone comment on these temperatures and pressures, please. ie if any look poor or if all okay:

    There are 3x systems: The first one is R22 and the other two were converted to R417a/MO59. I just wanted to know if they are looking okay as regards these figures.

    a) This R22 system seems a bit low on pressures and the FCU temperature differences look a bit shy at 8degC. Am I right that this system is short of gas?

    R22 Mitsubishi Electric Twin System
    PUH-4YKSA (3Ph)
    Condenser on temp: 19 degC, off: 27 degC

    Pressure HIGH Side: 12bar
    Pressure LOW Side: 2.9bar
    Current/Phase: 4 Amps


    Cassette #1:
    On temp: 19 degC, Off: 10.9 degC
    Diff = 8.1 degC (weak?)

    Cassette #2:
    On temp: 19 degC, Off: 11.1 degC
    Diff = 7.9 degC (weak?)
    ---------------------------------------------------

    b) This next system is on R417a. Seems good with FCU temp differences of 12 degC but the pressures seem low-ish.

    R417a Mitsubishi Electric Twin System
    PUH-4YKSA (3Ph)
    Condenser on temp: 22.8 degC, Off: 27 degC

    Pressure HIGH Side: 11 bar
    Pressure LOW Side: 2.2 bar
    Current/Phase: 4 Amps

    Cassette #1:
    Model: PLH-3GKHB
    On temp: 20 degC, Off: 7.8 degC
    Diff = 12.2degC (good)

    Cassette #2:
    On temp: 21 degC, Off: 8.6 degC
    Diff = 12.4 degC (good)
    --------------------------------------------------

    c) This R417a system seems barely okay with FCU temp differences of 10 degC and the pressures look low-ish, I think.

    R417a Mitsubishi Electric Single System
    Model: PUH-3YKA (3Ph)
    Condenser on temp: 20.7 degC, Off: 29 degC

    Pressure HIGH Side: 14.7bar
    Pressure LOW Side: 1.9bar
    Current/Phase: 4 Amps

    Cassette:
    On temp: 20.8 degC
    Off temp: 11.3 degC
    Diff = 9.5 degC (okay)

    Any Comments please?



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 3 systems, R22 +R417a -- Pressures look okay?

    a, seems to be s.o.g
    b,4.3 cond delta T is too low should be around 10c both hp and lp are to loww should be 15-20 barg hp 4-5 barg lp check your evap coil you'll probably find it s frosting over
    c, again pressures are too low

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 3 systems, R22 +R417a -- Pressures look okay?

    Do we get some commission on this purchase deal?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: 3 systems, R22 +R417a -- Pressures look okay?

    a) This R22 system seems a bit low on pressures and the FCU temperature differences look a bit shy at 8degC. Am I right that this system is short of gas?

    hi there interseted to know but i thought a 8-10 degree differential between air on and air off on the evap is okay??

    however it does seem like it is SOG

    Also are these systems all non inverter??


    cheers lee
    Last edited by moondawn; 25-06-2010 at 06:37 PM.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: 3 systems, R22 +R417a -- Pressures look okay?

    As with any refrigeration system, be it A/C or fridge, the pressures should be converted to temperature via the comparator and then your decision about whether it is operating correctly should be based on this.

    If it is R22 or some other gas, It does not really matter, it is the temperature that is important not the pressure. Superheat or Subcooling are based on temperature not pressure.

    We see questions on here about what pressures the system should be running at. If you consider what temperature you want your evaporator to be, then it is an easy task to convert this to pressure for a particular gas which will give you the answer

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: 3 systems, R22 +R417a -- Pressures look okay?

    If you think it is short, weight it out and see, then you can leak test it with ofn if it is.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 3 systems, R22 +R417a -- Pressures look okay?

    Quote Originally Posted by monkey spanners View Post
    If you think it is short, weight it out and see, then you can leak test it with ofn if it is.
    Might be tricky, his bio states the OP is a buyer not a techy.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. Efficient Tri-Generation Systems
    By Kevin_N in forum New Technologies
    Replies: 2
    Last Post: 07-03-2010, 11:16 PM
  4. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Replies: 31
    Last Post: 09-02-2009, 04:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •