    Hi all,
    Do you have experienced using air duct attached on the condenser? Will it cause air-cond to be reduced cooling capacity?
    I have been assigned to do calculation of cooling capacity loss from the air-cooled condenser with or without air duct as attached.
    The system is indoor unit: Liebert PEX (Precision Air Conditioner), outdoor unit: air-cooled condenser
    What factor that we need to do calculation e.g. CFM (in/out), temperature (in/out), etc.?
    The air duct's dimension is 850 x 850 x 1000 mm.
    We use this because customer needs to reduce noice from condenser.
    Please advice.
    Aug 2007
    Sydney
    52
    1,083
    23
    Re: Loss Cooling Capacity?
    I have seen many ducted condensers - but not for noise reduction, to minimise hot air recirculation. For noise reduction I have seen larger slower fans installed. Each system is different and perhaps it wouldn't take a tech too long to remove the hood, measure then put it back on and measure, considering its size. A discharge duct will sometimes increase cooling capacity.
    11,024
    As per Tesla, you may need to change the condenser to one that will handle the increase in resistance.
    Jun 2007
    South Africa
    66
    120
    Standard fans on aircooled condensers are designed to remove air from the condenser in the easiest form, without any restriction!
    If you need sound attenuation, consult the necessary manufacturer. Increase in fan pressure, without increase in airflow will decrease condensing capabilities.
    I am not always right, but I'm never wrong!
    Jun 2005
    Romania
    213
    I agree with the post before me, but to answer your question of calculation you have to do the next calculation:
    Get the air volume of the condenser (preferably from the manufacturer ) , calculate the pressure drop in the elbow, reduction, and duct length.
    By taking the fans specifications (pressure drop curve) and calculate what is the actual air volume of the fan for the special conditions (or you can skip all the above and directly measure the air volume in your case).
    And then from the condenser's specifications you should find what is the capacity in the specified conditions (air volume of the fan) and extract the difference
  1. cooling capacity
    By Ahmed_LNG in forum Refrigerants
    Last Post: 13-05-2010, 03:25 AM
  2. Replies: 30
    Last Post: 25-04-2010, 12:40 PM
  3. Sensible Heat Factor / capacity of Inverter split Systems at part load?
    By Greengrocer in forum Technical Speculations
    Last Post: 09-02-2009, 04:57 PM
  4. Compressor loading, cooling, and range of operation.
  5. Regulation of cooling capacity
    By npaisnel in forum Domestic
    Last Post: 08-02-2002, 11:22 PM