    cspenard Guest

    Pump Alignment



    In the next week I am going to have to align the 3 chilled water pumps for the new Trane screws my company just installed. Problem is, it's been ages since I've done one and I want to do it the correct way, not just use a straight edge. My company also doesn't have 5K to drop on a laser tool, so any advice or direction to a good alignment website would be appreciated.



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Pump Alignment

    Laser tool not needed! A dial indicator does well.
    Look up this link and it will tell you all you need to know.
    http://www.carlylecompressor.com/Fil...ent_lowres.pdf

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Pump Alignment

    Thanks NH3LVR
    I d.loaded and checked it out and it's a goodie.

  4. #4
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Pump Alignment

    Great book, thanks NH3LVR..

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: Pump Alignment

    Great reference book, thanks very much.

  6. #6
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Pump Alignment

    Very nice NH3LVR!


    But a small tip, always ALWAYS! allign the machine sideways before you check the height.

    if the machine is off sideways, they height will be off as well.

    When I align machines, the first thing I do is make them parallel, even if they are off center.

    when they are parallel I move the motor sideways and try to keep it within the parallel as I move it sideways.


    Once you have the motor clocked in within the sideways tolerance you can start worrying about the height.
    -Cheers-

    Tycho

  7. #7
    cspenard's Avatar
    cspenard Guest

    Re: Pump Alignment

    Thanks for the advice and thanks for the link NH3LVR it's very much appreciated.

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Addition of a heat pump to solar heating system
    By rt29781 in forum Heat Pumps
    Replies: 24
    Last Post: 23-01-2010, 08:46 AM
  3. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  4. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Replies: 7
    Last Post: 08-08-2008, 05:13 PM
  5. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •