Got called to a DX milk tank on R22 but someone had previously changed the txv and fitted an R134a one....
I checked the standing pressure and looked it up on my trusty slide rule and it confirmed R22 pressures (so the refrigerant hadn't been changed too) so i chucked a new Tex2 and n'3 orifice (5.3 kw) on it.
I have been trying to work out what the R134a valve would be doing and i think it would be thinking that the superheat was way too low and would move to a closed position, what do you guys think?
It had a n'6 orifice in it (10kw), and i think it would have just worked like a fixed orifice system.
The superheat pixie had not been at the adjuster though
Jon
25-06-2010, 11:24 AM #2
Re: Wrong Txv for refrigerant type
Oh and it had been like this for three years or so and the customer hadn't noticed any loss of cooling duty
Jon
25-06-2010, 01:01 PM #3
The main different is the refrigerant in the sensing bulb. Apart from that, I think they are pretty much the same so if it was tuned correctly, I wouldn't worry too much but would change it the proper one.
25-06-2010, 04:37 PM #4
I think you are right, the valve construction looks the same, just the charge in the bulb is different. With the sporlan ones that were original equipment on these tanks i just change the element/bulb, easier and cheaper than a new valve.
I was just wondering how the system would run with the wrong valve fitted.
Jon
breaker type?
By tait71 in forum ElectricalReplies: 24Last Post: 05-09-2010, 04:39 AM -
Carrier Split Type
By Mik in forum Trouble ShootingReplies: 4Last Post: 23-01-2010, 09:16 PM -
vertical oil separator or horizontal type?
By cygbob in forum Industrial CompressorsReplies: 6Last Post: 30-04-2009, 10:13 PM -
How do you determine type of refrigerant in the system?
By tomtom in forum RefrigerantsReplies: 11Last Post: 12-02-2009, 09:06 AM -
earth leakage
By sid in forum ElectricalReplies: 33Last Post: 11-07-2008, 07:58 PM