    Wrong Txv for refrigerant type



    Got called to a DX milk tank on R22 but someone had previously changed the txv and fitted an R134a one....

    I checked the standing pressure and looked it up on my trusty slide rule and it confirmed R22 pressures (so the refrigerant hadn't been changed too) so i chucked a new Tex2 and n'3 orifice (5.3 kw) on it.

    I have been trying to work out what the R134a valve would be doing and i think it would be thinking that the superheat was way too low and would move to a closed position, what do you guys think?

    It had a n'6 orifice in it (10kw), and i think it would have just worked like a fixed orifice system.

    The superheat pixie had not been at the adjuster though

    Jon



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Wrong Txv for refrigerant type

    Oh and it had been like this for three years or so and the customer hadn't noticed any loss of cooling duty

    Jon

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Wrong Txv for refrigerant type

    The main different is the refrigerant in the sensing bulb. Apart from that, I think they are pretty much the same so if it was tuned correctly, I wouldn't worry too much but would change it the proper one.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Wrong Txv for refrigerant type

    Quote Originally Posted by chemi-cool View Post
    The main different is the refrigerant in the sensing bulb. Apart from that, I think they are pretty much the same so if it was tuned correctly, I wouldn't worry too much but would change it the proper one.
    I think you are right, the valve construction looks the same, just the charge in the bulb is different. With the sporlan ones that were original equipment on these tanks i just change the element/bulb, easier and cheaper than a new valve.

    I was just wondering how the system would run with the wrong valve fitted.

    Jon

Similar Threads

  1. breaker type?
    By tait71 in forum Electrical
    Replies: 24
    Last Post: 05-09-2010, 04:39 AM
  2. Carrier Split Type
    By Mik in forum Trouble Shooting
    Replies: 4
    Last Post: 23-01-2010, 09:16 PM
  3. vertical oil separator or horizontal type?
    By cygbob in forum Industrial Compressors
    Replies: 6
    Last Post: 30-04-2009, 10:13 PM
  4. Replies: 11
    Last Post: 12-02-2009, 09:06 AM
  5. earth leakage
    By sid in forum Electrical
    Replies: 33
    Last Post: 11-07-2008, 07:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •