    Capillary size



    Hi All,
    I hav replaced a rotary compressor in a window Ac. The first one had stalled. The replacement comp is manufactured by Siam Compressor Industries Thailand. The original comp was by same company. The Ac is a 1,5 TR unit.
    Before starting the unit i want to make sure that the capillary is right. The unit has two caps of .064 " ID having length of 41.5 inches.

    What is the correct cap size for the compressor having model no RH313VADT

    Thanks in anticipation.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Capillary size

    I don't think that you can base the size of the capillary line on the size of the compressor.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: Capillary size

    Hi Brian,
    How do I ascertain that the cap size is correct.
    I ask this because the unit had low low side pressure of 54 psig at hi pressureof 200 psig, and the unit was running at full load amps.
    Appreciate your response.

  4. #4
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Capillary size

    Kssoin,
    If you have replaced the same model compressir then there could not be any problem with the cap. size . Capillary size should be caluculated based on mass flow rate and operating pressures/ temperatures. Your AC suction and discharge pressures are too low. Have you changed the old filter frier and capillary?

  5. #5
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: Capillary size

    Quote Originally Posted by sendhilkmar View Post
    Kssoin,
    If you have replaced the same model compressir then there could not be any problem with the cap. size . Capillary size should be caluculated based on mass flow rate and operating pressures/ temperatures. Your AC suction and discharge pressures are too low. Have you changed the old filter frier and capillary?
    Hi Sendhil Kumar,
    It is a hyundai 1.5 TR. The original comp was 19*** BTU/Hr manuf by M/s Siam Compressor Industries.
    I could not get that comp. Got this one which fits the foundation bolts perfectly. This is a 18500 BTU/Hr comp.
    this is a 31.3 cc per rev as per the spec.
    So what should the cap size be?
    Yes i replaced the filter drier and the caps, i dont know jf they would suit this compressor.
    I have also changed the orientation of the drier. Previously the cap tube end was 90 Deg vertical. Now I have made it abt 20 to 60 Deg downwards. (A Learning from this forum).
    If i increased the pressures to abt 60 psig at the suction(after the evap. the unit drew current over the max value of 9.4 Amps. At peak ambient (43 Deg C )at midday the current was abt 11 Amps.

    Appreciate your response.
    Last edited by kssoin; 24-06-2010 at 03:32 PM.

  6. #6
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Capillary size

    you may cut down the length; Try with 32" length #2 of the same bore. what was the discharge pressure @ the time of 60 Psig suction?

  7. #7
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: Capillary size

    Quote Originally Posted by sendhilkmar View Post
    you may cut down the length; Try with 32" length #2 of the same bore. what was the discharge pressure @ the time of 60 Psig suction?
    Hello Sendhil Kumar,
    Thanks for the reply,
    At 60 psig the high pressure was abt 225 psig.
    Now that compressor had failed. I got the compressor cut from a local machinist,
    The bearing at the bottom is stuck at a particular point in the revolution.
    Yes i will try with 32".
    Tell me what should be the suction line pressure after the evaporator, given the high ambient we have in delhi abt 42 - 44 Deg C, also a low evap temp will cause freezing during high humidity days coming ahead.
    Regards
    Last edited by kssoin; 26-06-2010 at 06:46 AM.

  8. #8
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Capillary size

    Kssoin,
    At 45C ambient the discharge pressure goes around 300 Psig and suction would be around 85 Psig. Frosting will take place at lower suction pressures (below 55 psig).

  9. #9
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: Capillary size

    Quote Originally Posted by sendhilkmar View Post
    Kssoin,
    At 45C ambient the discharge pressure goes around 300 Psig and suction would be around 85 Psig. Frosting will take place at lower suction pressures (below 55 psig).
    Hi Sendhil Kumar,
    I fixed the caps yesyterday and charged the ac with abt 1 Kg R 22.
    By the time i finished it was evening. I am getting 63 psig after evap and 250 psig at the liquid line. I measured the subcoolong it was 4 to 5 Deg K and the the super heat was abt 12 and the lowest was abt 9 Deg K. There was a lot of sweating on the suction line. The compressor current was 8 Amps. I will now check these values in the morning. The lowest evap in air temp was 17 Deg C.
    Since subcooling is low can some more of refrigerant be charged ?

  10. #10
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: Capillary size

    You can charge little bit refrigerant; but maintain the superheat min. 10 C. Do you mean return Ait temp 17C or wet bulb temp. 17C

  11. #11
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: Capillary size

    Quote Originally Posted by sendhilkmar View Post
    You can charge little bit refrigerant; but maintain the superheat min. 10 C. Do you mean return Ait temp 17C or wet bulb temp. 17C
    17 deg C was the lowest Air in at the evaporator.

  12. #12
    Join Date
    Apr 2010
    Location
    Delhi
    Age
    67
    Posts
    26
    Rep Power
    0

    Re: Capillary size

    Quote Originally Posted by Brian_UK View Post
    I don't think that you can base the size of the capillary line on the size of the compressor.
    Hi Brian,
    I had contacted the compressor manufacturers and they've sent me a pdf manual for the rotary compressors. it is a 2.9 MB file that cannot be posted. There is a section on Capillary tube selection of six pages that are abt 700 KB . I will post these six pages on yor PM .
    As per these from chart 1
    i get for a cooling of 2300 Kcal/hr i get a cap tube length of 1.8 meters for an ID of 0.064".
    From chart 2 for condensing temp of 45 Deg C and 5 Deg C of subcooling gives a correction factor of 0.8. so the length is 1.8*0.8= 1.44 meters. (Two number capillary tubes.)
    In chart two we have subcooling lines and Dryness % lines. What is Dryness % in this context.
    Regards
    I cannot attach the pages in pdf form as each is larger than 100 KB. How do I post these?
    Last edited by kssoin; 16-07-2010 at 08:28 AM.

Similar Threads

  1. Capillary tube size, refrigerant, oil
    By desA in forum Fundamentals
    Replies: 53
    Last Post: 23-02-2010, 05:11 AM
  2. size capillary for any application & refrigerant
    By benijoseph in forum Technical Speculations
    Replies: 12
    Last Post: 07-06-2009, 10:00 AM
  3. Capillary tube size!
    By mkpo in forum Fundamentals
    Replies: 25
    Last Post: 18-04-2009, 12:07 PM
  4. :rolleyes: capillary tube size in distributor?
    By abbasi in forum New Technologies
    Replies: 2
    Last Post: 08-07-2006, 03:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •