    AHU Oversize



    Hi all, recently i have got my existing AHU replaced from 60RT to 80RT. From the replacement, the motor kW, chilled water supply demand, etc... have indirectly increased too. However i am having my doubt on the AHU performance, whether my supplier has oversize the 80RT AHU.

    By comparing the measured pressure drop with the PD inside the catalog, how much deviation in the reading should i get to determine whether the AHU is oversize or undersize, and please enlighten me should there be other ways which i can determine whether my AHU is oversize. Btw, my AHU is being tagged onto a VSD.

    Would appreciate for any kind input.

    Thank You.



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: AHU Oversize

    You need to measure a lot more than static press. All measurements should be made with VSD at 100% and VAVs at 100%. Need to measure air volumes L/S, SPress b4 filt, b4 coil, b4 fan, aft fan and areas. With and without fresh air. Measure fan speed and compare with manufactures data. Then the duct measurements. It's not a small task and should involve a consultant with balancing tech taking measurements. Of course when the AHU is increased so will motor kW and CW. Is the VSD rated for increased motor? I have taken all these measurements for a consultant who passed them onto and engineer for design.

Similar Threads

  1. Oversize Relief Valve
    By Dacosta in forum NH3
    Replies: 1
    Last Post: 05-09-2008, 11:35 AM
  2. Oversize Piston in Open Type Recip. Compressor
    By imranmd in forum Commercial
    Replies: 29
    Last Post: 29-07-2007, 07:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •