Thread: no one has an answer
22-06-2010, 01:04 PM #1
circa '65 carrier, 40t a/c system, 06e
had a blown valve - all new valves/plates/gaskets, 500micron, 74#virgin r22, sight glass 1/2 full, 85ambient, 365/70, liq line 83deg, suct line 87deg, discharge 275deg, manually operated 3rd sol v to full open - brought discharge to 255deg, suction to 90, head same
asap(rebuilders) and senior techs are scratching their heads
diagnosis?!!!
22-06-2010, 01:35 PM #2
Re: no one has an answer
45 years old. Give it a merciful burial.
22-06-2010, 02:13 PM #3
Hi mpowerdog and welcome to the forum.
Making a few assumptions here - air cooled cond, Three TEVs stacked one on top of the other, AC, high superheat.
Measure each superheat in turn as loading then all three when fully loaded. Is there OA dampers and what position? What is the on/off coil temps average? Sounds like (with the info given) TEV superheat problem. What controls the SValves?
Also check the carlyle manual http://www.scribd.com/doc/13484919/C...Service-Manual for compressor faults and other useful info. Let us know how you go. Almost forgot - I think it takes 24 running for the valves to bed in and seat properly.Last edited by Tesla; 22-06-2010 at 02:30 PM. Reason: Info added
22-06-2010, 07:48 PM #4
Welcome mpowerdog.
Tesla may well have a good point about the Valves needing to bed in.
Isolating the suction and discharge and observing the rate of pressure equalisation. May well prove his point?
Please look at the attached.
Has anyone considered that the internal pressure relief valve may of blown? (section ss item 31 )
Particularly as you mention valve issues previously!
Just one of many thoughts
IE If the comp was running for any length on time with a blown valve, surely the rings could of glazed the liner affecting the seal between both?
Is your loading / unloading gear working as it should?
Good luck and as Tesla asks please let us know the outcome.
26-06-2010, 02:56 AM #5
Is the 365/70 a typo or actual. Awfully high for 22!!!!
I found where you get paid to answer HVAC
By tonyhavcr in forum Computers & the InternetReplies: 2Last Post: 24-03-2010, 06:07 PM -
Anti Vibration Pads the answer?
By superswill in forum Technical DiscussionsReplies: 4Last Post: 06-08-2009, 03:50 AM -
Can any one tell me the answer for this....
By padmarajan27 in forum Technical SpeculationsReplies: 2Last Post: 07-05-2009, 12:23 PM -
question i cant find an answer to
By jaeck75 in forum FundamentalsReplies: 4Last Post: 21-11-2008, 01:51 PM -
No Body have An Answer !!!
By Mahmoud in forum FundamentalsReplies: 21Last Post: 18-09-2005, 05:36 PM