    circa '65 carrier, 40t a/c system, 06e

    had a blown valve - all new valves/plates/gaskets, 500micron, 74#virgin r22, sight glass 1/2 full, 85ambient, 365/70, liq line 83deg, suct line 87deg, discharge 275deg, manually operated 3rd sol v to full open - brought discharge to 255deg, suction to 90, head same

    asap(rebuilders) and senior techs are scratching their heads

    diagnosis?!!!



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: no one has an answer

    45 years old. Give it a merciful burial.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: no one has an answer

    Hi mpowerdog and welcome to the forum.
    Making a few assumptions here - air cooled cond, Three TEVs stacked one on top of the other, AC, high superheat.
    Measure each superheat in turn as loading then all three when fully loaded. Is there OA dampers and what position? What is the on/off coil temps average? Sounds like (with the info given) TEV superheat problem. What controls the SValves?
    Also check the carlyle manual http://www.scribd.com/doc/13484919/C...Service-Manual for compressor faults and other useful info. Let us know how you go. Almost forgot - I think it takes 24 running for the valves to bed in and seat properly.
    Last edited by Tesla; 22-06-2010 at 02:30 PM. Reason: Info added

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: no one has an answer

    Welcome mpowerdog.
    Tesla may well have a good point about the Valves needing to bed in.
    Isolating the suction and discharge and observing the rate of pressure equalisation. May well prove his point?
    Please look at the attached.
    Has anyone considered that the internal pressure relief valve may of blown? (section ss item 31 )
    Particularly as you mention valve issues previously!
    Just one of many thoughts
    IE If the comp was running for any length on time with a blown valve, surely the rings could of glazed the liner affecting the seal between both?
    Is your loading / unloading gear working as it should?
    Good luck and as Tesla asks please let us know the outcome.
    Grizzly

  5. #5
    Join Date
    Jan 2010
    Location
    South
    Posts
    15
    Rep Power
    0

    Re: no one has an answer

    Is the 365/70 a typo or actual. Awfully high for 22!!!!

Similar Threads

  1. I found where you get paid to answer HVAC
    By tonyhavcr in forum Computers & the Internet
    Replies: 2
    Last Post: 24-03-2010, 06:07 PM
  2. Anti Vibration Pads the answer?
    By superswill in forum Technical Discussions
    Replies: 4
    Last Post: 06-08-2009, 03:50 AM
  3. Can any one tell me the answer for this....
    By padmarajan27 in forum Technical Speculations
    Replies: 2
    Last Post: 07-05-2009, 12:23 PM
  4. question i cant find an answer to
    By jaeck75 in forum Fundamentals
    Replies: 4
    Last Post: 21-11-2008, 01:51 PM
  5. No Body have An Answer !!!
    By Mahmoud in forum Fundamentals
    Replies: 21
    Last Post: 18-09-2005, 05:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •