    Daikin FFQ50BV1B



    Daikin FFQ50BV1B + RXS50BVMB.
    Fault Code U4, seems to be bad communication.
    Strange phenomena: on same main power supply but on a different breaker, the VD controlled compressor (grounded) of a VRV failed also this morning.
    For the Daikin pro's: what do you think, change both (in- and outdoor) PCB boards?
    Does someone has the manual of FFQ50BV1B and RXS50BVMB


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin FFQ50BV1B

    This is strange that both systems have gone down sharing the same power supply.
    check to see if the varisters are blown on the outdoor printed circuit board, this will indicate over voltage or a dropped neutral.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Daikin FFQ50BV1B

    No, no varistors blown, only 1 compressor grounded.
    Call for the split was in teh late afternoon and for the VRV around 10 o'clock this morning. This is the second VFD compressor in 5 months and the 3th in 12 years on the same site with total 11 outdoor VRV units.
    In that building on the same main supply are at least 200 PC's connected and testing devices in electronic labs. If there should be a problem with the supply, then I suspect also faults in other systems apart from the VRV's.
    Last edited by Peter_1; 21-06-2010 at 09:13 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •