    Dear All,

    I need help for the following question and thanks in advance,

    “how do we determine pressure inside the cold room assuming the cold room is at sea level, and 101.3 kPa. The cold room is operating at -20 deg C. Would room pressure be affected by fan coil defrosting?”

    Thanks,
    Lauren
    Last edited by chillin out; 21-06-2010 at 08:27 PM.



  2. #2
    Join Date
    Mar 2010
    Location
    India
    Posts
    100
    Rep Power
    15

    Re: Cold Room Pressure

    Are you aware of forum rule for multiple thread
    Last edited by sachin230; 21-06-2010 at 10:50 AM.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Room Pressure

    Unless the room is air-tight, the pressure in the room is exactly the same than outside of it.

    Don't post the same question over and over.

  4. #4
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Cold Room Pressure

    Quote Originally Posted by NoNickName View Post
    Unless the room is air-tight, the pressure in the room is exactly the same than outside of it.
    Sorry, I disagree with your opinion.
    In air-tight room with the temperature -20 C pressure in room will less than out of the room where temperature is about 20 C.
    On account of thise, in cold storage install equalizing valve.
    Air pressure you can find:
    p=ro*R*T/M
    p - pressure of air [Pa]
    ro - density of air [kg/(m^3)]
    R - universal gas constant = 8.31
    T - temperature of air [K]
    M - molecular mass of air =0.028 [kg/(m^3)]
    In some places will have to think ...

  5. #5
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Cold Room Pressure

    Cold room will under negative pressure compared to outside as we do not take any fresh air and gets infiltrated by door opening or closing.

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Cold Room Pressure

    The pressure would vary throughout the room due to air motion from the fan and turbulence through coil. Also vapor pressure deficit would have an effect from moisture removal via defrost. It can be calculated from psychometric chart with Pressure Volume Temperature relationship. Myth Busters did an interesting demonstration on pressure/weight in a truck with with pigeons. On average as Sridhar1312 wrote above is correct.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Room Pressure

    Exactly, that's why I said "UNLESS the room is air-tight".

  8. #8
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Cold Room Pressure

    Quote Originally Posted by NoNickName View Post
    Exactly, that's why I said "UNLESS the room is air-tight".
    some youngsters are so eager to replay that they don't take the time to read the questions fully.

    they are young and still learning, we have to forgive them.

    Ice

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Cold Room Pressure

    Sounds like a college question to me.

  10. #10
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Re: Cold Room Pressure

    Sorry as I am new to RE, will be careful next time and understand the rule...
    Sorry for any inconvenience caused..

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Cold Room Pressure

    A coolstore should a have pressure relief vent, that being the case the static pressure is the same. (as stated by nonickname)
    You will however get velocity pressure changes within the room (as stated by tesla)
    After defrost, well that down to how the system is set up, but lets say poorly, "no fan delay or drip down time" fan starts with a hot coil, then a large pressure increase occurs through the coil "cold air expanding while being warmed" Boyles Law????? along with a velocity pressure wave.
    The more inresting one is a chest freezer, open the lid, then close quickly. leave a few seconds, try to open again. If the freezer has agood seal you can not open.
    The warm air is cooled (reducing in volume) causing a vacuum inside.

  12. #12
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Re: Cold Room Pressure

    Dear All,

    Thanks for yr reply.
    But based on our cold room design, we have 3 evaporators and each time defrosting (with hot gas at 45 deg C) take 30mins with fan is turn off for only one evaporator and the remaining 2 evaporators still operated as usual to maintain the cold room temperature at -20 deg C. Between, fan delay also applied.
    We also have a vent port to equalize the cold room pressure.

    With such design, would the cold room pressure still be affected by fan coil defrosting?
    How much different if compared with outside pressure and cold room pressure at the same sea level?

    I did some calcualtion and found out the cold air(-20 deg C) density is higher than normal air (33 deg C) density... hence the cold room air pressure is greater than atmospheric pressure (14.7 Psia).

    Please kindly advise me. Many thanks.

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Cold Room Pressure

    Quote Originally Posted by Lauren View Post
    Dear All,

    Thanks for yr reply.
    But based on our cold room design, we have 3 evaporators and each time defrosting (with hot gas at 45 deg C) take 30mins with fan is turn off for only one evaporator and the remaining 2 evaporators still operated as usual to maintain the cold room temperature at -20 deg C. Between, fan delay also applied.
    We also have a vent port to equalize the cold room pressure.

    With such design, would the cold room pressure still be affected by fan coil defrosting?
    How much different if compared with outside pressure and cold room pressure at the same sea level?

    I did some calcualtion and found out the cold air(-20 deg C) density is higher than normal air (33 deg C) density... hence the cold room air pressure is greater than atmospheric pressure (14.7 Psia).

    Please kindly advise me. Many thanks.
    Please read what you have written, you have the answer.
    I have given you a small clue

  14. #14
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Cold Room Pressure

    Quote Originally Posted by NoNickName View Post
    Exactly, that's why I said "UNLESS the room is air-tight".
    Sorry, don't see "UNLESS"

    some youngsters are so eager to replay that they don't take the time to read the questions fully.

    they are young and still learning, we have to forgive them.
    icecube51, thanks for yours understanding.

    I did some calcualtion and found out the cold air(-20 deg C) density is higher than normal air (33 deg C) density... hence the cold room air pressure is greater than atmospheric pressure (14.7 Psia).
    Besides density also there is temperature of air... Check your calculations...
    In some places will have to think ...

  15. #15
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Question Re: Cold Room Pressure

    Hi,

    Here is my calculation,
    1) Air at -20 deg C;
    Density air = 1.4135 kg/m3
    Temp= 253.15 K
    Air constant, R= 286.9 J/Kg.K
    P= density x temp x air constant
    P= 1.4135(253.15)(286.9)
    P= 102.66kPa
    P= 14.9 Psia

    2) Air at 33 deg C;
    Density air = 1.154 kg/m3
    Temp= 306.15 K
    Air constant, R= 286.9 J/Kg.K
    P= 101.36kPa
    P= 14.7 Psia

    Please kindly advise me if you think my calculation is inaccurate. Many thanks

  16. #16
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Room Pressure

    Quote Originally Posted by mad fridgie View Post
    please read what you have written, you have the answer.
    I have given you a small clue

    rtoflmao :d

  17. #17
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Question Re: Cold Room Pressure

    Hi Mad Fridgie,

    I got what u meant but recently I encountered a case said that my cold room pressure is muiltiple times greater than outside almospeheric pressure with the mentioned design...

    I have no concrete pressure data in cold room at -20 deg C, hence want to seek you guys expertise on this.

    After calculated the air pressure for cold room and normal temperature and found out that the air pressure slightly higher in cold room altho knowing that density in cold room is higher than normal air temperature.

    Thanks

  18. #18
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Cold Room Pressure

    Maybe you should indicate your problem, as we all seem to be struggling with what you are asking.
    This then may make more sense.
    Yes cold air is more dense, so the pressure at the bottom of a static head level will be higher than the ambient.
    Think like a cup holds the static head, if you continue to fill the cup it will overfllow so at the top the pressure is equal to the ambient

  19. #19
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Cold Room Pressure

    Quote Originally Posted by Lauren View Post
    Hi,

    Here is my calculation,
    1) Air at -20 deg C;
    Density air = 1.4135 kg/m3
    Temp= 253.15 K
    Air constant, R= 286.9 J/Kg.K
    P= density x temp x air constant
    P= 1.4135(253.15)(286.9)
    P= 102.66kPa
    P= 14.9 Psia

    2) Air at 33 deg C;
    Density air = 1.154 kg/m3
    Temp= 306.15 K
    Air constant, R= 286.9 J/Kg.K
    P= 101.36kPa
    P= 14.7 Psia

    Please kindly advise me if you think my calculation is inaccurate. Many thanks
    If you have air-tight room you put in thise room warm air, close door and cooling air.
    If room air-tight than mass of cold and warm air be the same (volum of room also the same).
    Density of cold and warm air is the same, because mass and valume is the same (ro= mass/volume of room)
    Than:
    at 33 C and 40% rh density = 1.12 kg/(m^3)
    p=1.12*8.31*306.15/0.028=101.8 kPa
    at -20 C
    p=1.12*8.31*253.15/0.028=84.1 kPa
    In some places will have to think ...

  20. #20
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Re: Cold Room Pressure

    Pardon me for my ignorance, so may I presumed that you are agreed with my cold room pressure calculation which cold room pressure at -20 deg C is greater than ambient pressure with my current cold room condition?

    And the cold room pressure wouldnt be affected much with fan coil defrosting?

    Thanks for your expertise reply and comments.

  21. #21
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Cold Room Pressure

    Quote Originally Posted by Lauren View Post
    Pardon me for my ignorance, so may I presumed that you are agreed with my cold room pressure calculation which cold room pressure at -20 deg C is greater than ambient pressure with my current cold room condition?
    No, no and once more NO...
    In air-tight cold room after cooling pressure will be 84.1 kPa.
    Ambient pressure (at 33 C) is 101.8 kPa.
    If there isn't vent port which equalize cold room pressure than at this temperature you may don't open the door.
    You have vent port in your room, than pressure in room = ambient pressure... many peple tell you about it in this theme
    In some places will have to think ...

  22. #22
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Room Pressure

    Quote Originally Posted by Lauren View Post
    Pardon me for my ignorance, so may I presumed that you are agreed with my cold room pressure calculation which cold room pressure at -20 deg C is greater than ambient pressure with my current cold room condition
    You must be challenged. I fully sympathise with you.

  23. #23
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Re: Cold Room Pressure

    Hi Aik,

    Sorry as I missed out yr reply as I was posting my query before seeing yr reply.
    Thanks for highlighting me regarding the densiry air...

  24. #24
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Re: Cold Room Pressure

    Hi Nonickname,

    Is fine with me as I'll treat this as my learning path. I am a new bird in refrigeration field... No pain no gain....(",)

    Thanks all for the guidance.

  25. #25
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Cold Room Pressure

    I'm just wandering. How can we design(and build) air tight cold room? Usually, this room has evaporator and evaporator has a drain and drain goes outside of this cold room.

  26. #26
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Room Pressure

    Quote Originally Posted by Segei View Post
    I'm just wandering. How can we design(and build) air tight cold room? Usually, this room has evaporator and evaporator has a drain and drain goes outside of this cold room.
    With a peristaltic condensate pump and a non return valve

  27. #27
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Cold Room Pressure

    Quote Originally Posted by NoNickName View Post
    With a peristaltic condensate pump and a non return valve
    Definitely, you can do that. But you need a water strainer... May it is better water trap. You don't need pump, strainer, non return valave, vent port....

  28. #28
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Re: Cold Room Pressure

    Thank you all for the expertise comments...
    I will close this thread now....

    Lauren

  29. #29
    Join Date
    Jun 2010
    Location
    Malaysia
    Posts
    10
    Rep Power
    0

    Re: Cold Room Pressure

    guess I will wait for 1 more day to make sure that "Segei" & "nonickname" have end their discussion here...
    Thx.

  30. #30
    Join Date
    Mar 2010
    Location
    Dammam
    Posts
    83
    Rep Power
    15

    Re: Cold Room Pressure

    He definitely answered his own question.
    All industrial aircoolers have drain pipes that is connected down to the waste pipe via P-traps to prevent foul air from going back into the rm. and keep the pressure atmospheric.
    Some cold storage rms. especially blast freezes have vacuum breakers inside to prevent vacuum pressure as what mad fridgie explained.
    Last edited by ref717; 24-06-2010 at 04:59 PM.
    <"No one is so smart, they just stay with problems longer and use their imagination">

  31. #31
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Room Pressure

    Quote Originally Posted by Segei View Post
    Definitely, you can do that. But you need a water strainer... May it is better water trap. You don't need pump, strainer, non return valave, vent port....
    None of that is needed. Or am I missing something about your post?

  32. #32
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Cold Room Pressure

    Quote Originally Posted by NoNickName View Post
    None of that is needed. Or am I missing something about your post?
    My point is that drain of typical evaporator will equalize the pressure inside and outside.

Similar Threads

  1. deep freeze cold room prob
    By cadwaladr in forum Commercial
    Replies: 3
    Last Post: 20-06-2010, 09:55 AM
  2. Insulation for Cold Room
    By tjk2007 in forum Fundamentals
    Replies: 25
    Last Post: 19-03-2010, 02:54 AM
  3. Calcualting Room Pressure
    By tjk2007 in forum Fundamentals
    Replies: 5
    Last Post: 18-11-2007, 11:07 PM
  4. LG Capacitor - Room not cold
    By kelamel in forum Trouble Shooting
    Replies: 8
    Last Post: 21-10-2006, 10:50 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •