    I am having troubles with the EXV (electronic expansion valve) on circuit A of a Carrier 30GT090 chiller.
    The EXV continuously cycles, the measured superheat at the compressor suction sensor ranges between 5 deg F and 40 deg. F. The Service manual list total superheat at 30degF, (10deg after the chiller plus 15-20degF from the motor winding.)
    I've tested and inspected the EXV and all works ok. The temperature sensors all check ok and the sight glass is clear so why is the valve continuosly overshooting?
    The EXV on circuit B is working fine, maintaning right around 30degF superheat.
    Any suggestions will be apprecieated.
    Dan
    Below are compressor stats when I was troubleshooting this morning. Outside air temp was in mid 50s.
    Compressor A Running Conditions:
    suct pressure: 40 psi approx
    Disch Pessure: 140 psi approx
    Chilled water entering temp: 29 degf
    Chilled water leaving temp: 27degf
    Saturated suction temp:13
    Compressor return gas temp:varies 5 to 40F
    Condensing temp:68F
    Compressor B Running Conditions:
    suct pressure: ? not recorded
    Disch Pessure: 155 psi approx
    Saturated suction temp:17degf
    Compressor return gas temp:47degf
    Condensing temp:69degf
    Sep 2003
    ISRAEL
    72
    4,248
    Re: EXV Hunting
    Hi Dan.
    Although I have never played with one of these, It seems to me that from what you explaining, that the problem is in the controls
    To completely eliminate the doubt of the EXV, change the wires with the other one only for a minute and just to make sure that it operates OK.
    Check all the connections of all the wires to make sure that no loose connection is giving you these results.
    If none of this will help, then the problem is in the control.
    Is it powered with ComfortLink Controls?
    Chemi
    Dec 2004
    LEBANON
    44
    854
    21
    Re: EXV Hunting
    Was this EXV replaced before ? or it's the original one ?
    I suggest that you check the stepper motor wires for faults . . .
    Please let us know what happens next .
    Dan H's Avatar
    Dan H Guest
    Re: EXV Hunting
    Botrous;
    Both EXV valves have been replaced, but not by our company. I don't have any records to show why. The stepper motor checks out ok.
    Chemi;
    This chiller has a Flotronic Control System.
    I checked all the wiring and the valve operation per the service manual and found no problems.
    I like your idea of swapping wires to the other EXV. The controller is contiuously overshooting, which makes it seem like the valve is moving to slow.
    I will be working on the unit again tommorrow, I'll let you know what happens.
    Dan
    Dec 2004
    LEBANON
    44
    854
    21
    Re: EXV Hunting
    ok Dan I am looking forward to hear what will happen . Hope that you will find the problem and fix it.
    Sep 2003
    ISRAEL
    72
    4,248
    Re: EXV Hunting
    One more thing Dan,
    Most of these step motors, work on 24 acv, the command is 1 to 10 volts.
    It is not hard to disconnect it from the controller and check it to see that it operates OK.
    If it works OK, then no doubt, the problem in the controller.
    If it doesn't work smoothly, replace it.
    Having two units work from one controller, will make it easier on you to eliminate the parts that are in fine working order.
    Chemi
    rbartlett's Avatar
    rbartlett Guest
    Re: EXV Hunting
    I think hunting should be banned...
    cheers
    richard
    Oct 2003
    5,630
    34
    Re: EXV Hunting
    The Carrier guys can connect very easily a portable PC on the unit and adapt the PID algorithm for the EXV.
    We had the same problem some years ago.
    To measure an EXV: just check the 4 windings of the stepper motor which has to be 4 times the same value (mostly mentioned on the technical papers delivered with the unit)
    Is evaporator correct loaded, pumps running, water filters not clogged
    Another strange thing on Carrier Chiller with multiple compressors, controlled by that bloody Prodialog electronics (how easy was in those days without all that fancy electronics): the first compressor is the master, the other the slaves. The Prodialog monitors the resistance of each crankcase heaters If the heater of the master fails, the whole unit is shut down!!. If this chiller is in a production line, then you're serious in trouble. Just switch the heaters temporarily so that the unit can run again.
    Feb 2005
    Aberdeen
    48
    168
    Re: EXV Hunting
    Make sure the compressor is pumping correctly as I have come across problems with exv's on this type of carrier chiller.
    Is the chiller actuating any fault codes?
    Jase
    Oct 2003
    5,630
    34
    Re: EXV Hunting
    Quote Originally Posted by Jase
    Make sure the compressor is pumping correctly...
    How do you do this or change it in case it isn't?
    Dan H's Avatar
    Dan H Guest
    Smile Re: EXV Hunting
    Thanks to all for your comments.
    It turns out that Jase was correct....the compressor disharge valves were damaged. I installed new valve plates today and the unit is working fine.
    I took me four days of testing and troubleshooting before I began suspecting the compressor to be the problem.
    I ran all of the factory service manual tests on the processor, I tested and swaped all sensors with known good ones...nothing had an effect on the EXV.
    I noticed compressor motor amps were inconsistent.. going from 30 amps to 65 amps. (FLA =57)
    I spoke with a compressor rebuilder, he said bad discharge valves were probably the cause of the high motor amps.
    The Flotronics Processor measures the superheat temerature entering cylindar head "A". As discharge pressure is forced back down the suction port due to the bad valve, the temperature reading fluxuates...causing the EXV to compensate for the temperature change.
    Anyhow..I am glad to have this one working. I am a controls specialist first, with ok mechanic abilities. I just couldn't see how the compressor could be at fault, but it makes sense now.
    Dan
    Jun 2005
    54
    Re: EXV Hunting
    I had one do something like that .It was showing large superheat due to gas shortage but only faulted once!! on low gas charge since the gas charge pressure sensor was on the high side!! and after the system filled with air it read a good head pressure again.kept showing erratic or eventually high superheats though I think you can swap tx valvbes by swapping 2 plugs around pretty easy to try I think??
  1. Hunting Etc.
    By subzero*psia in forum Hobbies
    Last Post: 19-09-2010, 01:40 PM
  2. job hunting
    By neil sailes in forum Chit Chat & Service Stories
    Last Post: 13-10-2005, 09:00 PM
  3. hunting???
    By Friobernal in forum Fundamentals
    Last Post: 18-05-2004, 02:00 PM
  4. Job hunting...
    By morpheas_24 in forum Chit Chat & Service Stories
    Last Post: 17-06-2002, 11:07 AM
  5. Subcool and Superheat
    By Abe in forum Trouble Shooting
    Last Post: 04-03-2002, 05:50 AM