Converting A Daikin Split From R22 To R417a
When recharging with R417a I see the initial charge as recommended by Dupont is 85% of the intial charge then add as required up to the full R22 charge.
My question is when checking the S/C and S/H what figures would I expect? I intend to check right before the the Expansion valve in the OU and get a figure of 1-2K (probably H.P. around 200psig) and superheat at the indoor cassette of 6-8K (suction of about 60psig to give a bubble point of 0*C and dew point of about 6*C).
H.P. measured from discharge schrader inside case, L.P. at service port, liquid port not used for these measurements. The figures I've taken off a mollier chart.
I've messed around with refrigeration equipment checking these figures but never on an A/C unit so wondered if that is how you would do it and expect those figures?
The original charge was lost due to leakage so I wont be able to use these figures as a baseline as suggested by DuPont on this reftrofit guide http://www.agas.com/product/files.ph...34207_4502.pdf
Cheers,
Andy.Last edited by Tayters; 20-06-2010 at 09:44 AM.
Health and safety first..........unless I'm in a hurry.
Similar Threads
-
Daikin split short cycling after leak repaired
By Tayters in forum Air ConditioningReplies: 16Last Post: 17-06-2010, 12:23 PM -
filter for cassette type daikin split FHYC71B7V1
By sork in forum Air ConditioningReplies: 1Last Post: 28-04-2010, 10:13 PM -
Daikin twin split trouble
By dave ldms in forum Air ConditioningReplies: 1Last Post: 25-02-2010, 06:34 PM -
Daikin split problem (any ideas)
By airconjohn in forum Air ConditioningReplies: 14Last Post: 17-02-2008, 08:40 PM -
Daikin twin split
By Lippygit in forum Trouble ShootingReplies: 2Last Post: 28-07-2007, 06:28 PM