    Using TEV without Sensing Bulb



    Hi there,

    We are using sporlan TEV type DAE 10, DAE 15 & AAE 20 for our chiller room evaporators. the system was on service for about 2 years.

    Recently we notice most of our TEV sensing bulb having severe defect due to the material not comparetable (Brass/cooper). we are waiting for the vendor to comment since last 2 month.

    At the moment, we still need our system to be operate to maintain the tempreture for our product by manually adjusted / set the TEV adjusting stem. we manage to control the desire temperature.

    The stupid question here, if we can control or set the desire temperature by trotelling the size of the orifice CV , why we still need to use TEV.

    rgds

    TQ



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Using TEV without Sensing Bulb

    if the bulb is missing, the refrigerant from the TEV's diaphragm upper side is gone. TEV will shut.
    It can not work.

    You can use other manufacturers TEV's.

  3. #3
    Join Date
    Feb 2010
    Location
    England
    Age
    59
    Posts
    243
    Rep Power
    16

    Re: Using TEV without Sensing Bulb

    Quote Originally Posted by MazlanZ View Post
    Hi there,

    We are using sporlan TEV type DAE 10, DAE 15 & AAE 20 for our chiller room evaporators. the system was on service for about 2 years.

    Recently we notice most of our TEV sensing bulb having severe defect due to the material not comparetable (Brass/cooper). we are waiting for the vendor to comment since last 2 month.

    At the moment, we still need our system to be operate to maintain the tempreture for our product by manually adjusted / set the TEV adjusting stem. we manage to control the desire temperature.

    The stupid question here, if we can control or set the desire temperature by trotelling the size of the orifice CV , why we still need to use TEV.

    rgds

    TQ

    if the valve is now set to work without the bulb what will happen is the valve will act like an automatic expansion valve.
    For the system to work correctly there is some fluctuation in the temperature and a working TEV can compensate for any temp change.

    With the setup you have at the moment it may work and it may deliver a reasonable temp but any safety and control has been removed from the system.

    For what it will cost, get the thing replaced for a new TEV and let it work the way it was meant to.

    coolrunnings

    .

  4. #4
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    58
    Posts
    522
    Rep Power
    19

    Re: Using TEV without Sensing Bulb

    I think the sporlan type have got interchangeable heads, just make sure the gas type or the colour of the head match. If you have adjusted the superheat setting to compensate for no bulb, then you will have to throttle the stem valve shut so refrigerant flows, and then slowly adjust it to the desired setting. If you just fit a new head to it without adjustment, it may flood the evaporator and damage the pot.

  5. #5
    Join Date
    May 2010
    Location
    Malaysia
    Posts
    12
    Rep Power
    0

    Re: Using TEV without Sensing Bulb

    Thanks Guys for your comment,

    By the way any body have the experience in repairing or overhouling the VILTER VSS 1201 & 1851 single compressors ?. I'm not familiar with those type, if for twin screw type I'm easily fix it with single handed regardless what ever brand or size.

    mazlanz

  6. #6
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    58
    Posts
    522
    Rep Power
    19

    Re: Using TEV without Sensing Bulb

    Quote Originally Posted by chilliwilly View Post
    I think the sporlan type have got interchangeable heads, just make sure the gas type or the colour of the head match. If you have adjusted the superheat setting to compensate for no bulb, then you will have to throttle the stem valve shut so no refrigerant flows, and then slowly adjust it to the desired setting. If you just fit a new head to it without adjustment, it may flood the evaporator and damage the pot.
    Sorry its meant to read so no refigerant flows.

Similar Threads

  1. Use of Dry/Wet bulb when design a ac system
    By happychan314 in forum Air Conditioning
    Replies: 13
    Last Post: 13-04-2009, 04:31 PM
  2. How many forum posters does it take to change a light bulb....
    By taz24 in forum Chit Chat & Service Stories
    Replies: 7
    Last Post: 04-02-2008, 08:05 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 02:25 PM
  4. tev bulb in immersion well?
    By angryk in forum Fundamentals
    Replies: 3
    Last Post: 20-01-2003, 10:42 PM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •