    Feb 2009
    telford
    2,092
    33
    deep freeze cold room prob
    i have a cold store about 8mtrsx8mtrsx3 mtrs it has two evaps,two 5hp prestcold condensing units with semi-hermetic compressors,the evaps are searle 240 running on r22 ,the prob i have is on one of the condensing units it has in my opinion slightly high suction pressure with the room at -10 i have 30psi suction pressure 180/190 psi head a full sight glass,the body of compressor is warm alike to the temp of warm water,a lack of refrigeration capacity,the other system is working fine in line driers were changed 2 weeks ago,on pump down test via receiver outlet takes too long[in my opinion]8minutes approx,shut suction pressure drops rapid but does not hold vac for long,ambient 70/80f i am leaning to valve leakage in compressor,any ideas thanks in advance.
    Jun 2007
    darwin
    13
    Re: deep freeze cold room prob
    To test the compressor what you could do is attach your gauges to the compressor both high side and low side. swicth compressor off. close suction and discharge service valves. open low side of hand gauges to let the gas out of the low side only through your gauges. obviously you would reclaim this. if the discharge pressure drops you know you have a leaking valve. if it remains the same the valves are ok.
    the other thing is to check your superheat if its -10 then suction pressure would be 24 to 27psi. your head pressure seems fine for the tempreture you have indicated. i would say superheat adjustment and check your sight glass.
    scotland
    756
    passing on the head for sure, is it a iceland store?
    Feb 2009
    telford
    2,092
    33
    just an update,went back yesterday and it was working fine?,and no not at an iceland store,its a food maker lol,they make donner kebabs,whats the prob ? its been playing up according to the custumer for about 2 months,it normally runs at -20 and recent -12c,
  1. 2 degree C cold room evaporator question.
    By almichieuk in forum Trouble Shooting
    Last Post: 02-07-2010, 11:23 AM
  2. Capacity Calculation for Deep Freeze cold store
    By Asheesh in forum Technical Speculations
    Last Post: 08-08-2009, 09:40 AM
  3. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Last Post: 13-03-2009, 01:49 AM
  4. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Last Post: 12-03-2006, 09:20 PM