Results 1 to 2 of 2
  1. #1
    Pete S's Avatar
    Pete S Guest

    York YS chiller water connections left vs right hand config



    I have been asked to install a used York
    YSCBCA S-CHB5 water cooled chiller. All of the condenser and chilled water connections are on the right side of the unit.

    For ease of installation, can I swap the ends and make the water connections on the left side?

    Background info:
    I have another York YSBBBBSI GA-A that is generally an identical unit except the water connections are on the left hand side. I called other manufacturers and was told that the ends can be swapped but there will be an 8% loss of capacity. York never responded.
    The literature makes no reference to left or right hand units, which makes me suspect that the ends are interchangeable. Any thoughts? Thanks

    Pete S



  2. #2
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: York YS chiller water connections left vs right hand config

    if they can be exchanged for the caps

Similar Threads

  1. york chiller oil
    By 1mikeefc1 in forum Technical Discussions
    Replies: 0
    Last Post: 24-07-2009, 03:59 PM
  2. York Chiller Fault
    By kifayat in forum Trouble Shooting
    Replies: 8
    Last Post: 11-07-2009, 02:55 PM
  3. small water chiller with blocked tubes
    By multisync in forum Air Conditioning
    Replies: 6
    Last Post: 11-06-2009, 03:07 PM
  4. york chiller not running
    By cool it in forum Trouble Shooting
    Replies: 21
    Last Post: 16-06-2006, 12:13 AM
  5. Comments on this please
    By Robearbam in forum Fundamentals
    Replies: 8
    Last Post: 18-04-2005, 05:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •