    Question BP spill & Mini-split demand/market



    Hello All,
    There are a lot of residences in the northeast using hydronic heat, so given the BP disaster and ongoing oil situation, why shouldn't these folks be a prime market for mini-splits? I'm thinking about getting back into installing these systems. Folks are getting old, need air conditioning, they have no ductwork currently, and need a localized backup heat source.

    Anyway, I've not done refrigeration work since the mid 90's using R22, and I need to upgrade my stuff, so I'm thinking about a YellowJacket 69080 vac gauge, and a yellowjacket BruteII model 46013 to replace/upgrade my gauges. Would anyone care to comment on if the 4 hose manifold is worth the extra money, or if it's actually that practical to use? I'm thinking about using that 4th hose just for the vacuum pump and gauge, but will the line collapse? I used to use a copper vacuum line, but mabye there's a new better way.

    Also, I'm wondering what I'm getting into with the mini-splits, do they have proper schraeder valved service ports already installed, or does the installer have to braze them in? At least my torch still works.
    Thanks,
    John B.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: BP spill & Mini-split demand/market

    3/8" vac hoses do not collapse.

    Splits have access ports pre-fitted.

    New gases, R410a, run at higher pressures than you are used to, get gauges/manifolds suitable.

    Upgrade your nitrogen gauge, test pressures could be up to 40 bar, 580psig.

    Torque spanners required for flare nuts.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: BP spill & Mini-split demand/market

    I'd say the 4 port gauge is worth the extra spondolicks.
    Had to hand mine back when changing company and noticed the 4 port easier to use with less hose swapping.

    Don't forget when vaccing out you can connect the yellow line to the bottle and vac that out as well to save purging the line.

    Splits over here are pre-charged and have a schrader built on to the suction service valve - kind of like a rotalock. Bigger units have one on the liquid valve also. Most will have a schrader on the discharge inside the unit as well, but don't count on it. Wanted to check one today (on a Sanyo) and there wasn't one!
    Last edited by Tayters; 15-06-2010 at 11:44 PM.
    Health and safety first..........unless I'm in a hurry.

  4. #4
    helenk579's Avatar
    helenk579 Guest

    Re: BP spill & Mini-split demand/market

    Quote Originally Posted by elmdas View Post
    Hello All,
    There are a lot of residences in the northeast using hydronic heat, so given the BP disaster and ongoing oil situation, why shouldn't these folks be a prime market for mini-splits? I'm thinking about getting back into installing these systems. Folks are getting old, need air conditioning, they have no ductwork currently, and need a localized backup heat source.

    Anyway, I've not done refrigeration work since the mid 90's using R22, and I need to upgrade my stuff, so I'm thinking about a YellowJacket 69080 vac gauge, and a yellowjacket BruteII model 46013 to replace/upgrade my gauges. Would anyone care to comment on if the 4 hose manifold is worth the extra money, or if it's actually that practical to use? I'm thinking about using that 4th hose just for the vacuum pump and gauge, but will the line collapse? I used to use a copper vacuum line, but mabye there's a new better way.

    Also, I'm wondering what I'm getting into with the mini-splits, do they have proper schraeder valved service ports already installed, or does the installer have to braze them in? At least my torch still works.
    Thanks,
    John B.
    I also think so.

  5. #5
    Join Date
    Dec 2007
    Location
    n.ireland
    Age
    45
    Posts
    38
    Rep Power
    0

    Re: BP spill & Mini-split demand/market

    Quote Originally Posted by Brian_UK View Post
    3/8" vac hoses do not collapse.

    Splits have access ports pre-fitted.

    New gases, R410a, run at higher pressures than you are used to, get gauges/manifolds suitable.

    Upgrade your nitrogen gauge, test pressures could be up to 40 bar, 580psig.

    Torque spanners required for flare nuts.
    think your a wee bit out with the nitrogen gauge,mitsi electric recommend doin a strength test to 600psi for 20 mins..correct me if i,m wrong

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: BP spill & Mini-split demand/market

    Quote Originally Posted by aircool View Post
    think your a wee bit out with the nitrogen gauge,mitsi electric recommend doin a strength test to 600psi for 20 mins..correct me if i,m wrong
    Aw, what's 20psi between friends?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Servicing a LG Mini Split 410a
    By wrangoth in forum Trouble Shooting
    Replies: 8
    Last Post: 28-04-2010, 06:59 PM
  2. Mini split system heating, but not cooling well.
    By tirider in forum Heat Pumps
    Replies: 7
    Last Post: 06-11-2009, 09:17 PM
  3. Amcor mini split control board
    By alive2live in forum Air Conditioning
    Replies: 2
    Last Post: 25-10-2009, 01:06 AM
  4. Need help trouble shooting mini split ac error code "e4"
    By grindrx in forum Air Conditioning
    Replies: 5
    Last Post: 23-07-2009, 08:57 PM
  5. Klimaire mini split installation
    By JohnK in forum Air Conditioning
    Replies: 3
    Last Post: 19-05-2009, 07:51 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •