    Compressor above condenser.



    Dear all, placing condenser with liquid receiver below compressor (~5 meters below) cause that installation does not function? Could you give me theoretical background concernig that issue please?

    Regards

    Pawel
    Attached Images Attached Images



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor above condenser.

    What does not function in your set up?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Compressor above condenser.

    Hi there,

    Most probably you have a problem with liquid line which goes up 5m. You have to calculate the correct liquid line size and also required sub cooling so that a solid liquid line reaches the TEV.

    Cheers
    Even Einstein Asked Questions

  4. #4
    Join Date
    Jan 2007
    Location
    Poland
    Age
    49
    Posts
    12
    Rep Power
    0

    Re: Compressor above condenser.

    Thx for expl.
    Brg Pawe.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor above condenser.

    Quote Originally Posted by Pawel_Wisnik View Post
    Dear all, placing condenser with liquid receiver below compressor (~5 meters below) cause that installation does not function? Could you give me theoretical background concernig that issue please?

    Regards

    Pawel
    I don't see any problem with this setup.
    But what IS your problem exactly?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Compressor above condenser.

    probably a low pressure problem on the LP inlet of the compressor..... i think?

    Ice

  7. #7
    Join Date
    Jan 2007
    Location
    Poland
    Age
    49
    Posts
    12
    Rep Power
    0

    Re: Compressor above condenser.

    Quote Originally Posted by Peter_1 View Post
    I don't see any problem with this setup.
    But what IS your problem exactly?
    Hi Peter,

    I am forced to apply such layout in one of my sites within a couple a weeks to come, but in the meantime I heard an opinion that such setup did not work at all (but without explanation why it did not and what was the main problem), in my opinion there is no threats in it, but just to be sure I also dropped post here to see opinion from you, opinions that I appreciate very much .

    Regards

    Pawel

  8. #8
    Join Date
    Dec 2002
    Location
    South Africa
    Age
    83
    Posts
    41
    Rep Power
    0

    Re: Compressor above condenser.

    Possible accumulation of oil in receiver?

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor above condenser.

    Make sure your line going up is large enough in diameter and if you want to use EEV's on your evaporators, try to install a subcooler (PHE) after your receiver.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Compressor above condenser.

    Quote Originally Posted by Pawel_Wisnik View Post
    Hi Peter,

    I am forced to apply such layout in one of my sites within a couple a weeks to come, but in the meantime I heard an opinion that such setup did not work at all (but without explanation why it did not and what was the main problem), in my opinion there is no threats in it, but just to be sure I also dropped post here to see opinion from you, opinions that I appreciate very much .

    Regards

    Pawel
    May be it was a case when compressor above condencer and receiver near the compressor (above condencer)?
    In some places will have to think ...

  11. #11
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Compressor above condenser.

    i am more thinking in the line of the compressor. problems whit the oil return. i don't think there was a refrig mensioned in this topic.

    Ice

  12. #12
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    20

    Re: Compressor above condenser.

    It should work, If it is not working give the pressure reading of LP and HP?

    RGDs

  13. #13
    Join Date
    Jan 2009
    Location
    Australia
    Age
    60
    Posts
    108
    Rep Power
    16

    Re: Compressor above condenser.

    Provided the line size is right, it should work ok. Oil return can be a problem in condensers lower than the compressor particularly if the ambient conditions are low and head pressure control is poor. It often turns turns to sludge and sits in it occupying condenser area. Then a young tech comes along - sees no oil in the compressor and promptly adds another litre or two which also ends up in the condenser and so on it goes.

    Best plan is to probably think about an oil separator to take care of the oil issues, make sure the lquid line has a low enough pressure drop and it should work fine.

  14. #14
    Join Date
    Jan 2007
    Location
    Poland
    Age
    49
    Posts
    12
    Rep Power
    0

    Re: Compressor above condenser.

    Quote Originally Posted by Peter_1 View Post
    Make sure your line going up is large enough in diameter and if you want to use EEV's on your evaporators, try to install a subcooler (PHE) after your receiver.
    Hi Peter,
    I do so

    Regards
    Pawel

  15. #15
    Join Date
    Jan 2007
    Location
    Poland
    Age
    49
    Posts
    12
    Rep Power
    0

    Re: Compressor above condenser.

    Quote Originally Posted by icecube51 View Post
    i am more thinking in the line of the compressor. problems whit the oil return. i don't think there was a refrig mensioned in this topic.

    Ice
    Hi,
    in my opnion there should not be a problem with oil, it flows freely down to condeser via discharge line then within condenser and liquid receiver dissolves in refrigerant.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor above condenser.

    Indeed, you will not face oil problems and surely not in the discharge and liquid lines. Liquid will fush out all the oil
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Compressor above condenser.

    In my opinion there is one problem of your system.
    On summer ambient temperature may be high then room temperature where compressor situated. If compressor stop long time then its temperature may be smaller then condencer (and receiver). And refrigerant may migrate from receiver through condencer to head of compressor and condense there. When compressor start then may be hydraulic shock...
    In some places will have to think ...

  18. #18
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Compressor above condenser.

    always safe to mount an oiltrap evry 3mtr.

    Ice

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor above condenser.

    In upgoing liquid lines and flowing down discharge lines?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Compressor above condenser.

    A non-return valve in the liquid line outlet from the condenser would not be a bad idea...

  21. #21
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Compressor above condenser.

    in this case Peter, upgoing.

    Ice

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor above condenser.


    .........................

  23. #23
    Join Date
    Jan 2007
    Location
    Poland
    Age
    49
    Posts
    12
    Rep Power
    0

    Re: Compressor above condenser.

    Quote Originally Posted by Aik View Post
    In my opinion there is one problem of your system.
    On summer ambient temperature may be high then room temperature where compressor situated. If compressor stop long time then its temperature may be smaller then condencer (and receiver). And refrigerant may migrate from receiver through condencer to head of compressor and condense there. When compressor start then may be hydraulic shock...
    Hi
    in this case machniery room always is at equal or a bit higher temperature than ambient, even in summer time.

  24. #24
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor above condenser.

    An NRV will give you an additional DP in your liquid line and decrease overall system performance.
    Why you need it anyhow? What is its benefit?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  25. #25
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Compressor above condenser.

    When compressor stop, if temperature of condencer and receiver will bigger than compressor, than refrigerant in liquid phase will evaporate in condencer and condence near more cold compressor (migrate).

    Hi
    in this case machniery room always is at equal or a bit higher temperature than ambient, even in summer time.
    Then I don't see problems in your system...
    Last edited by Aik; 21-06-2010 at 06:46 AM.
    In some places will have to think ...

  26. #26
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Compressor above condenser.

    Quote Originally Posted by Gingerair View Post
    A non-return valve in the liquid line outlet from the condenser would not be a bad idea...
    In this system it would be better install check valve in the gas line on inlet to the condencer.

    always safe to mount an oiltrap evry 3mtr.
    Oiltraps don't stop migration...
    In some places will have to think ...

  27. #27
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Compressor above condenser.

    Quote Originally Posted by Aik View Post
    Oiltraps don't stop migration...
    but whit the migration of the refrig, some oil will return, so the compressor will always have some oil to work whit.

    Ice

  28. #28
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor above condenser.

    I don't see any problem except that subcooling must be enough to compensate for 0,63 bar pressure drop due to liquid column of liquid refrigerant in 5 m pipe.
    Oil is not of any concern if it is soluble with liquid refrigerant.

  29. #29
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Compressor above condenser.

    Quote Originally Posted by icecube51 View Post
    but whit the migration of the refrig, some oil will return, so the compressor will always have some oil to work whit.

    Ice
    In any case in Pawel_Wisnik's system oil trapes don't need on discharge line.

    I don't see any problem except that subcooling must be enough to compensate for 0,63 bar pressure drop due to liquid column of liquid refrigerant in 5 m pipe.
    Oil is not of any concern if it is soluble with liquid refrigerant.
    I have the same opinion...
    Last edited by Aik; 22-06-2010 at 06:39 AM.
    In some places will have to think ...

  30. #30
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor above condenser.

    Quote Originally Posted by nike123 View Post

    .........................
    In the Suva example, gas line, 33.9 psi at bottom and 34.1 psi at the top
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  31. #31
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor above condenser.

    ................................
    Deleted!
    You are right, it is mistake.
    Last edited by nike123; 22-06-2010 at 07:42 PM.

  32. #32
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor above condenser.

    Why then the bottom weights less?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  33. #33
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor above condenser.

    I think you misunderstand my last post. Deleted is my comment (which is wrong) that everything is OK on that Suva picture, because i did not paying attention at what is bottom and what is up.
    Than I confirmed that you are right.

  34. #34
    Join Date
    Jun 2010
    Location
    United Kingdom
    Age
    48
    Posts
    6
    Rep Power
    0

    Re: Compressor above condenser.

    Hi

    This is Gareth Jones

    Most probably you have a problem with liquid line which goes up 5m. You have to calculate the correct liquid line size and also required sub cooling so that a solid liquid line reaches the TEV.

    Regards,

    Gareth
    CNM ONLINE

  35. #35
    Join Date
    Jun 2010
    Location
    United Kingdom
    Age
    48
    Posts
    6
    Rep Power
    0

    Re: Compressor above condenser.

    Hi

    Most probably you have a problem with liquid line which goes up 5m. You have to calculate the correct liquid line size and also required sub cooling so that a solid liquid line reaches the TEV.

    Regards,

    Gareth
    CNM ONLINE

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. How to measure COP (evaporative condenser)
    By Juho in forum Technical Discussions
    Replies: 5
    Last Post: 04-06-2010, 07:08 PM
  4. Evaporative Condenser system COP
    By Juho in forum Commercial
    Replies: 0
    Last Post: 03-06-2010, 09:23 AM
  5. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •