    Cap tube for R23



    Hi there,

    Does anyone know a reference for cap tube sizing for R23? This is required for a cascade system down to -75°C evaporating temperature with 2.2kW capacity.

    Appreciate any help.

    Cheers


    Even Einstein Asked Questions

  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Cap tube for R23

    download " Dancap" , a free program from Danfoss.

    works fine.

    Ice

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Cap tube for R23

    Ice, Dancap doesn't work with R23
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Cap tube for R23

    Lana - post as many details as you have especially the mass flow rates and I will run it for you.

    Chef

  5. #5
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Cap tube for R23

    Quote Originally Posted by Peter_1 View Post
    Ice, Dancap doesn't work with R23
    oeps, forgot to check that one.
    thnx Peter.

    you see, we are learning every day something new here.

    Ice

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Cap tube for R23

    Thanks everyone,

    I had checked the Dancap before and it does not work with R23.
    Even Einstein Asked Questions

  7. #7
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Cap tube for R23

    Lana - I have a program that runs R23 and can run a scenario for you if you wish. I will need the pressures and Temps at the condenser and evap plus the mass flow rate. Although I can estimate the mass flow from the cooling load it would be better to have a precise figure. Any SC info would help and also if the condenser is oversized.

    Chef

  8. #8
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Cap tube for R23

    Based on these conditions
    R23, te=-75°C tc=-20°C capacity 2.12 kW suction superheat 20°K.
    The following results are shown for your system.

    You may be trying to push the duty a little too hard as a tube of 2mm is already 5m and it has gone sonic at the exit which is not advisable, however a smaller tube is shorter and the exit is even more of a problem and a bigger tube gets very long.
    A 2.3mm tube is 11m long!!!!!
    Setting Tc = -25C helps the duty to be manageble but that of course depends on your first stage?

    Hope it helps

    Chef
    Attached Images Attached Images

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Cap tube for R23

    Hi Chef, the programs looks good.
    just a question about this application, would installing 2 (or more) caps give better results. (or is just the nature of the application giving you the concerns)
    cheers
    Mad

  10. #10
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Cap tube for R23

    Quote Originally Posted by mad fridgie View Post
    Hi Chef, the programs looks good.
    just a question about this application, would installing 2 (or more) caps give better results. (or is just the nature of the application giving you the concerns)
    cheers
    Mad
    Hi Mad
    Very good point indeed and your absolutely right.
    These are the results for multiple tubes

    3 off 1.2mm by 3.5 m exit velocity is 151m/s
    2 off 1.5mm by 4.1 m exit velocity is 158m/s
    1 off 2mm by 5.7 m exit velocty is 171m/s

    So using multiple tubes can keep the velocity below sonic and give shorter tubes in the installation.

    4 off 1mm has the same exit as 1 off 2mm but 7 off 0.8mm is fine and tube drops to 2.2m.

    Interesting set of choices?

    Chef

  11. #11
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Cap tube for R23

    Many thanks for your reply.

    I am little bit confused. Can you clarify about the cap tube ID and length?
    Is it 2mm ID and 5.7m length?

    Thanks again.


    Is it
    Even Einstein Asked Questions

  12. #12
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: Cap tube for R23

    Lana - if you open up the little attachment I posted it does show the tube ID as mm and the length as m - both SI units. All other references to the tube are ID and length.

    Its too difficult to use OD of the tube as wall thicknesses vary from one to another manufacturer so the ID would be impossible to gauge.

    Chef

  13. #13
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Cap tube for R23

    Thanks a lot.
    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  2. Cap Tube Design Program - Results
    By Chef in forum Fundamentals
    Replies: 3
    Last Post: 01-09-2008, 09:49 AM
  3. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Replies: 4
    Last Post: 15-11-2007, 06:03 AM
  4. Coils - Inline vs Staggered tube
    By nh3simman in forum Fundamentals
    Replies: 15
    Last Post: 03-04-2007, 08:25 PM
  5. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •